Has anyone used the "Logix5000 Controllers as Masters or Slaves on Modbus" application solution from Rockewell (Publication CIG-AP129A-EN-P)? It is slightly confusing in that it tells you it ONLY supports Modbus RTU, but then the user protocol is ONLY ASCII. I just want to make sure this is going to work. It is a heck of a lot cheaper then adding a Prosoft card.
 
I've used the 1769-SM2 module to drive the Modbus RTU of AB drives. I have not driven directly from the com port though - kind of a bummer to lose your backup programming port.

With the 1769-SM2 I just followed the documentation and had no problems - it was so easy I can't even remember how it works. That app solution looks ugly (like most com programming on the AB's) - good luck
 
Jedft:
First, make sure you use application v2 that distributed with v17 or higher. V2 is also availabe in the Knowledgebase

Modbus serial has to flavors:
RTU - 8 bit protocol and ASCII 7 bit protocol that is not used anymore
Logix supports RTU only

To use Logix serial port you need to switch it to the "USER' mode that supports only "ASCII" protocol that has nothing to so with Modbus ASCII - just the same name.

Just load applicaiton and it will work without any modifications.
 
I have one application out there where I have a ML1100 and two VFD's communicating via Modbus RTU out of the ML1100's serial port. It's been in service for about 4 years and hasn't hiccuped since.

Greg
 
I have successfully used a CompactLogix as a Modbus RTU master through its own serial port. I used a Red Lion ICM5 RS-232/RS-485 converter to communicate with 3 or 4 slave devices. The sample code they provide was hard to understand but I locked myself in a room for a day and figured it out. One annoying thing about the sample code is that it is written for a ControlLogix processor, so if you have a lite version of the software you may not be able to open it and convert the processor. I had that problem at the time but can't remember how I worked around it.
 
I use the micrologix modbus rtu over serial all the time. for a controllogix I would use a digi one iap or plop down more money and use the prosoft card.
 
I wonder if I could go from CompactLogix to MicroLogix 1100 via DF1, then use the ML1100 for Modbus?? But ML only has 1 serial port right? So I guess maybe if I had Ethernet on the Compact I could do it, but I don't.... argh.
 
Last edited:
Let's take a step back:

Which CompactLogix controller model are you using ? I figure it's one with ControlNet or with only serial if you don't have Ethernet.

Do you need to have the CompactLogix be the Modbus Master or the Modbus Slave ?

What are the external devices the CompactLogix needs to communicate with ?

I've used both the example code and the Prosoft MVI69 module. For reliability and performance I strongly prefer the Prosoft module.
 
Ken, It's the 1769-L31 Dual Serial. We are trying to talk through a serial Radio to an iFix SCADA system. The controller will be a Modbus Slave.

Now we are looking at the Red Lion Data Station to do the conversion.

Cost is a serious consideration, but at the same time it has to work. That A-B application guide/example code is apparently quite misleading. Their tech support told us they have had 4 other calls this week telling them this doesn't work as they described in the guide. o_O
 
They already have 220 or so stations out there using Modbus. They don't want to change anything.
 
I've made calls to Prosoft insisting their device didn't work as described, too.... . until I found the mistakes I made.

If your application is straightforward, like reading a block of 4xxxx addresses and writing another block of them, I say use the Modbus code. Since it's using radiomodems it's likely that they are extremely forgiving of inter-character framing delay.

Download ModScan32 as a test client, and give it a shot.
 
I've tried this to,but it gives you so many programming trouble.
I've chosen for a Ethernet version of the CompactLogix, add an Anybus Communicator and your realy easy up and running with your ModBus.
If your communication is time criticall, please forget the serial port on a CompactLogix, I used it for DH485 communication to a servo system, and it was much to slow ( bit cycle time of about 0,4 sec. ).
 
Modbus serial has to flavors:
RTU - 8 bit protocol and ASCII 7 bit protocol that is not used anymore

Gee, I wish someone has told me that before I wrote my Modbus ASCII driver (just a few months ago). :ROFLMAO:

If you are going through modems (where there might be a short delay in transmission), then ASCII is the way to go. Any break in a RTU packet could be interpreted as the end of that packet (which would then be rejected).

Because ASCII uses a colon (":") for the start, and a CR/LF pair as the end of a packet, any delays in the packet (to a point) will be ignored.

http://www.lammertbies.nl/comm/info/modbus.html

And before someone says that nobody uses modems anymore, we just set one up for a client last week. :)
 
Will AB 1769-L32e communicate to a serial device set for Modbus protocol via RS232

Have a Allen Bradley 1769-L32e CompactLogix PLC and would like to use it to communicate to a DeltaV Serial Card- not programmable type. Will the 1769 communicate via the MODBUS RTU protocol correctly through it's Serial Port to the Serial Interface set as a slave device? THe DV Serial Card set as Master?
 

Similar Topics

Hi, I'm having an issue with a mircologix not transmitting out. The current setup is a mircologix 1400 connected to a Guardian 100 Radio...
Replies
1
Views
108
Anyone know how to bring modbus data from GE Multilin 850 the correct way? None of the registers are lining up and data is coming in with values...
Replies
4
Views
179
Hi Guys, Can ControlLogix with Modsim32 for Modbus Server Testing? I have ControlLogix via Anybus Modbus TCP and I need to Test the...
Replies
6
Views
308
I want to learn about modbus communication and I saw on another thread about inexpensive modbus relay units so I found it on Amazon along with a...
Replies
46
Views
7,225
Hi Guys, I'm searching for Modbus address register (mapping) for SCAME 27F (HS81) Fire and Gas Panel. I need to pull data from the panel to...
Replies
0
Views
759
Back
Top Bottom