VFD Harmonic Filters

jjnelson81

Member
Join Date
Apr 2007
Location
Springfield, MO
Posts
32
All,

I have searched the forum and cannot find anything to help answer my question. Regarding VFDs, what criteria is used to determine the type of filters needed for a VFD installation.

IEEE 519 has a ITHD of 5% at the PCC, but at a component level, when do you determine to use a line reactor, a line reactor and harmonic filter, a sinusoidal filter, etc. Are there applications where you would only need one type of filter vs. multiple and how is that determined?

Best Regards
 
There is a lot of gray area and some significant snake oil regarding harmonics and VFDs. The best way is to ask the drive supplier to run a harmonic analysis of your system. Most will do this without charge.

If you need IEEE-519 compliance there are many ways to do this. They include active front ends, reactors, and 18-pulse or similar drive architectures. I usually leave it up to the supplier. If tehy are willing to gaurantee compliance with a specific technology then you should be in good shape.
 
Tom is correct about suppliers running a harmonic analysis for you but, be prepared to provide transformer impedance, length of leads of all branches in the network, a list of all loads and their harmonic contribution to the network, and the drive harmonic characteristics.

With that, the harmonic content of the proposed system can be accurately predicted.

The problem, as I supposed has already become apparent to you is, how do I get all this data? A nasty problem indeed!
 

Similar Topics

Hello, It is mandatory to use VFD IF i use IE5 electrical motor? What happens If connect it directly as delta without VFD? Please look at motor...
Replies
1
Views
119
Hello, I am trying to setup on plc so If I enter 60 jph (job per hour) it will send the vfd hertz based on what jph is entered by...
Replies
2
Views
152
commentaire communiqué siemens s7-1200 avec vfd delta ? (cablage et sur tia portal )
Replies
0
Views
87
Hello, I'm trying to delve a little into rs-485 communications for a couple projects of mine. Until now I've been using a delta vfd and a delta...
Replies
2
Views
106
I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
Replies
1
Views
107
Back
Top Bottom