I need to run a 4-20mA signal from a Pro-face PLC to a AB Plc. The distance will be about 600ft. I plan on using 18 gauge shielded cable. Is this possible? What other suggestions would you have.

Thanks, Dave
 
If you can read via MSG command from AB PLC over a physical network (Modbus. RS-485, Ethernet, etc.), I would use that method. One cable could take the place of several shielded analog cables if you ever want to expand the capabilities of the network in the future
 
One thing to watch for is grounding. Running analog I/O from one controller to another you mught end up with the "-" tied to ground on both controllers. This can be worked around, but you need to watch for it.
 
I normally power up the signal source with a load before landing the other end to check the voltage differential to the receiver's common and ground. If that potential exceeds the specs for the card(s) or it's not described in the book as isolated, just add an isolator (signal conditioner).
 

Similar Topics

I am trying to use the 4-20 mA signals from a device whose user manual says that it outputs "isolated 4-20 mA". I only have spare PLC inputs in a...
Replies
3
Views
224
I'd like to talk this through a little: Relays are regularly used for PLC outputs, regardless of a need for signal conversion. But what about...
Replies
15
Views
949
Hi Everyone, We are EDAC Electronics Australia and we provide wireless automation solutions and I/O distribution products, with expertise in...
Replies
8
Views
771
Hi, When I use an interrupt OB (let's say OB38 which is processed every 10ms), does it read the state of the inputs at the time it is called, or...
Replies
18
Views
2,382
I have to carry out a programming where I have some valves and it has to meet these requirements: If the OPEN button is energized and the RETRO...
Replies
12
Views
1,512
Back
Top Bottom