Greetings!

I would like to ask if somebody here knows what is the meaning of a "LR" command at omron plc, am using CQM1 CPU 21 OMRON PLC. All used as NC/ NO contact (not output)

I cannot find on its help file. Thank you very much.

Sincerely,

Sheryl Caño
Philippines
 
Link Relays are pretty old - what PLC do you have?
It probaly has to be 8-10 years old.
Be really careful - if the network goes down the LR doesa not turn off!!!!!
 
Link Relays are pretty old - what PLC do you have?
It probaly has to be 8-10 years old.
Be really careful - if the network goes down the LR doesa not turn off!!!!!

The PLC is I quess is a 2nd hand, already used from Japan I think and was transported here (the machine). The model is omron cqm1 cpu21.

What you mean goes down? Trouble occur? If that will happen, what to do next? How to turn it ON / OFF and back to its normal case?

Actually, at auto operation, there is something wrong. There is a sequence that is being by pass. Say after curing time, a timer needs to be energized. Timr then energize. Then, a 2nd timer will ON to cool the product down. However, afer that, it has to be press up and then be release. Now, the operator will get the product. At that instance, it will not press up and release (slide out). Thus, i need now to study the whole sequence and understand where did it stop.

At the program, i saw an LR command in which i am not quite familiar yet. Is this an internal relay? Or, an outside field device? I cannot see it any on the help file available. I hope somebody in here can give some input.

Thank you very much.

Sincerely,

Sheryl Caño
 
Thank you for the meaning. However, I could you could refer me an manual to further explain. Is this an internal relay? Or, from a field device?

LR is an internal PLC data file.
Unless someone else can point you to it, You will have to find the Omron programming manual for that PLC family for a more detailed description.
 
Link Relays are pretty old - what PLC do you have?
It probaly has to be 8-10 years old.
Be really careful - if the network goes down the LR doesa not turn off!!!!!

Greetings!

When usually it is being energized if it started at the very first line (whar device needed in order to energize it if it is an internal relay?) No latching? What conditions will it usually turn ON/OFF? Like in other PLC (Mitsubishi), an M is an internal also but it needs an input device first before it can be turn ON like energizing first my push buttons then I can now used my internal relays. I am not so familiar with this "Link Relays" in Omron.

Can you attach here some of your handouts before? Or a website link will do.PLC I am using is OMRON CQM1 CPU 21.

Thank you very much.

Sincerely,

Sheryl Caño
Philippines
 
hello

LR=link relay same as internal relay (IR),previously i used LR for communicate 2 plc master(cqm1h) and slave(cpm1a)


eliskasim
kluangjohor
 
The usual reason for using LR is if there are two (or more) Omron PLCs connected together on a network.
The LR data area (words LR00-LR15 or bits LR00.00 - LR15.15) are automatically shared between the PLCs - no instruction required.

For example, PLC #1 may have an input 1.03 described as Stop_button_is _pressed, followed by an output instruction addressing bit LR2.01. (LD 1.03 OUT LR2.01)
In PLC #2 (or 3, or 4...) on the network, using LR2.01 as an INPUT (LD LR2.01) will read the data from PLC #1 as if it were a real input to PLC#2.

I have used LR areas to link and share data between 6 PLCs.
 
The usual reason for using LR is if there are two (or more) Omron PLCs connected together on a network.
The LR data area (words LR00-LR15 or bits LR00.00 - LR15.15) are automatically shared between the PLCs - no instruction required.

For example, PLC #1 may have an input 1.03 described as Stop_button_is _pressed, followed by an output instruction addressing bit LR2.01. (LD 1.03 OUT LR2.01)
In PLC #2 (or 3, or 4...) on the network, using LR2.01 as an INPUT (LD LR2.01) will read the data from PLC #1 as if it were a real input to PLC#2.

I have used LR areas to link and share data between 6 PLCs.

Greetings Mr. RoTaTech!

Currently, there is only 1 machine (and also one plc on it). It is from Japan (already too old more than 10 years I think) and they are trying to use the machine. I cannot understand why they are using the LR command and yet only transported 1 unit only.

1. Is it possible that although there's only 1 unit ( or there are 2 or 3), LR can still be used?
2. How could I trace (or know) that it is the 1st, 2nd or the 3rd unit?

3. When I troubleshoot it yesterday, I saw that there is a missing outside wire (an input) x101. Thus, it is the reason why the machine is not operating normally on auto mode (okay on manual mode). Thus, I removed that address in the PLC program. I cannot actually check what's that for. When I tried it, it is operating normally. However, see question # 4. Now, is it possible that that address came from the PLC prior to it?

4. On another selector switch and still at auto mode, I still miss some sequence, sad to say we cannot have its original as built wiring diagram. Is the reason is the LR commands?

Will LR works with or without other PLC? If it will not turn OFF (see above thread), what should I do?

Thank you very much. Hope to hear more.

By the way, are you more on omron plc programming? Mostly here in this circulation are all allen, siemens, etc.. I am more on Mitsubishi.

Sincerely,

Sheryl Caño
Philippines
 
Last edited:

Similar Topics

I have an issue with Power Flex 525 during running processing, the VFD stopped suddenly while the PLC and VFD connection ok, VFD does not have any...
Replies
1
Views
125
Hello everyone, I'm working with an old ACM3710 device and I'm encountering an issue with the data frames I'm sending over an RS232 connection...
Replies
5
Views
680
I have a customer that wants to print data anytime someone presses a button for a batch addition. They want to print quantities, person's name...
Replies
8
Views
3,016
Hi all, I had an interesting question posed to me. A developer asked me if there was a way to reset/reboot a plc via the plc itself. Not run/stop...
Replies
17
Views
6,497
Hi all. It's been a while since I last posted here :-) Looking for an advice on handling command/feedback mismatch during transitions. I have...
Replies
0
Views
1,041
Back
Top Bottom