compactlogix redundency with devicenet

Join Date
Dec 2010
Location
ALGERIA
Posts
12
hii everybody, i have 2 compactlogix L32E and two devicenet scanner for pumps control and i want to use redundency between them ,i'm a bigginer i tried but until now i can't do it ,so any body can help me please
 
The principal Redundant control system offered by Rockwell Automation is ControlLogix Redundancy. It uses ControlLogix (1756-L6x) controllers and ControlNet for I/O networking.

There is a DeviceNet-based "Easy Backup" mechanism for CompactLogix that provides a "hot standby" controller. It lacks many of the redundancy features that ControlLogix Redundancy provides, such as media redundancy, scan synchronization, data table cross-loading, and program edit cross-loading.

ControlLogix Redundancy is described in the ControlLogix Redundancy System User Manual, 1756-UM523. You must read and understand that manual and the Redundancy firmware release notes before attempting to implement ControlLogix redundancy.

CompactLogix DeviceNet "Easy Backup" is described in several Release Notes and application notes for the 1769-SDN module, including RA Knowledgebase document 50690.
http://rockwellautomation.custhelp.com/app/answers/detail/a_id/50690
 
hi again , can you please tell me where can i find firmware version 3 or late ,for devicenet 1769 sdn because its necessary for the backup thanks
 
hiii ,thanks for ur advice it work redundancy with 2 compactlogix and devicenet scanner ,but when i used factory talk for supervising i can't conect to one processor ,so if u have any idea about changing IP adress when the CPU change so factory talk connect with only the one who work thank you
 

Similar Topics

Hi everyone, i have a compact logic 1769-L18 PLC and I'm using FTalk View ME for the display. I wanted to do some visualization on Grafana. At...
Replies
1
Views
83
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
Replies
1
Views
88
Does this instruction calculate values during a single scan, or does it require number of scans based on element count in the array? For Example...
Replies
3
Views
109
Hello all, and thank you in advance for any assistance you may be able to provide! This is my first post, so if I need to reformat or change...
Replies
6
Views
380
We are trying to poll data coming from a PLC for remote monitoring we have the IP address of the PLC and the default port number and the path is...
Replies
25
Views
551
Back
Top Bottom