At this point you don't even know if what you want to do is possible with what you have.
mek_control's project sounds like a cascaded loop application where the servo controls the error between the valve set point generated by the outer temperature loop and the actual valve position. The inner loop part is not the problem.
mek_control said:
so i have to rise temperature but within specific time
Do you even know if the system is capable of heating with the specific time?
You don't need ramps. You need closed loop control with faster closed loop time constants.
you mean i have to modeling the system ??? i think that's difficult....
A crude model will do if you are lucky. If the plant time constant(s) are long you will not be able to heat the plant up quickly. If the plant gain is to low you will not even get to the higher temperatures. Dead time will also require the controller gains to be lower and this will slow response.
If the dead time is long then a Smith Predictor will be required. Unfortunately a Smith Predictor does require a model to predict with.
If you know the plants gain, time constant(s), dead time and the required response time I can calculate the gains for you and tell you what kind of PID to use in the PLC. Not all PIDs are created equal. You want a PID that will handle output saturation nicely and not suffer from integrator wind up.
all i need to have is closed loop to bring temp from existing degree to desired smoothly
I thought you to do it a a certain amount of time. So you need to increase the temperature quickly and smoothly without over shoot.
You can see you haven't provided enough information for good answers but now you know what to look for.