Hello all, i have a hydrolic cylinder that has to run at 1 inch per second till it hits full stroke (40 inches) than retract. i have a transducer in the cylinder that can measure the distance of the cylinders stroke. i need to develop a screen that shows the actual "real time" speed of the cylinder. how can i do this....

also, the cylinder has a 4-20mA directional valve that is controlled by an analog output card,the cylinder needs to auto correct itself if while running it starts to move faster than 1 in/s..could i accomplish this using a PID instruction??

i am using a plc-5. but they may make me swap the plc-5 to a micrologix 1100 due to the etherent capabilities

thanks for your help!!
 
Last edited:
Is the transducer 4-20mA? Are you talking about displaying the status of the cylinder on the 1100 screen? Are you using a seperate HMI? Why not get a ethernet converter for the SLC-5 or something like a red lion that does HMI and ethernet conversion. Is this new, a recycled SLC-5, or an upgrade????

Information please!
 
transducer is 4-20mA, i am talking displaying the real time speed on the current HMI which is a PV600 the HIM is simple i just want to display the tag that would be the speed. this is just a R&D project im working on the PLC-5 was a spare i had, i also have a micrologix1100 sittig at my desk, i chose the plc-5 just to test and be sure the processor and cards still worked; the MLX1100 i already knew it worked. all i want to know is can i determine the speed of the cylinder as it travels down and up. speed in inches per second.

hope thats enough info if you need more let me know
 
1) You can control cylinder speed with a PID loop.

2) Speed is ds/dt. Your cylinder is moving slowly, so use a timer and divide the distance moved in the time increment by the time increment. The result is velocity.
 
1) You can control cylinder speed with a PID loop.

2) Speed is ds/dt. Your cylinder is moving slowly, so use a timer and divide the distance moved in the time increment by the time increment. The result is velocity.

Equation for ds/dt is
(Old position - new position)/(old time - new time)

Dan Bentler
 
Lets talk about your controller and its capabilities first. What kind of position control and velocity control precision do you require? What kind of load are you moving and how is it supported? What size is the cylinder bore? What is the pump pressure

Depending on the answer to those questions you may need to seriously reconsider using a PLC - you may need a hydraulic motion controller since a PLC is is just plain too slow for precision hydraulic control.

Hopefully Peter will enter the discussion - be ready to answer some detailed questions. The more info we have the better answer you will get.
 
the speed is already accurate. the cylinder is mounted on a stand and just moves straight downward. they just want to see the speed of the cylinder and if something caused the speed to change auto correct it back to 1 in/sec.....currently the speed is at 1 in per second. just want to display that speed through the PLC onto an hmi screen.
 
I would recommend that you calculate the distance travelled every 1/2 second in raw units, then scale that number to inches per second for display. Most HMI won't update much faster than that anyhow, and if they do, a jittery number can be hard on the eyes.

So, every 1/2 second (self resetting TON), subtract the new_position from the old_postiion and store it as raw_counts_per_half_second, then MOV the new_postiion into the old_positiion register for the next calculation.

Then multiply that number by the units to inches scale factor times two (to get whole seconds).
 

Similar Topics

How do you execute speed or tension calculations in a PLC? Do you use a STI (Periodic task) to make sure the calculations are executed at the same...
Replies
9
Views
4,774
Does anyone have the formulas to calculate the number of boxes vs conveyer belt speeds? I have 5 automatic conveyer systems that according to the...
Replies
6
Views
3,841
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
Replies
1
Views
95
Hello, I am trying to setup on plc so If I enter 60 jph (job per hour) it will send the vfd hertz based on what jph is entered by...
Replies
2
Views
154
Sigh, DeviceNet noob... I have a 1756-L55, with a DeviceNet module, and 10 PF700 all commanded with DeviceNet. One of the PF700's blew up...
Replies
3
Views
129
Back
Top Bottom