I am learning PLC programming and can write a basic program but I am not sure where to start on this one. I have a Boiler they want to do a Blowdown on about 4 times a day, I have a DirectLogic 06 and a Automation Direct EA7 Touch Screen. I want to give them A place on the touch screen to input up to 4 different times and a duration. Such as 6am for 5 minutes and 13:00 hours for 7 minutes and so On. And that in turn will enable the blow down solenoid. The manual part I can figure out I just need someone to point me in the direction to start.

Any Help Appreciated
 
The manual part I can figure out I just need someone to point me in the direction to start.

Here is one way, there are many more. Copy the text below paste into notepad, save it, open a new instance of Direct Soft, click on "file", "import", "program" follow directions when prompted.

PLC 06

// Rung 1
// Address 0
#BEGIN COMMENT
"http://www.plctalk.net/qanda/showthread.php?t=60705"
""
"I am learning PLC programming and can write a basic program but I am not sure where to "
"start on this one. I have a Boiler they want to do a Blowdown on about 4 times a day, I "
"have a DirectLogic 06 and a Automation Direct EA7 Touch Screen. I want to give them A "
"place on the touch screen to input up to 4 different times and a duration. Such as 6am for "
"5 minutes and 13:00 hours for 7 minutes and so On. And that in turn will enable the blow "
"down solenoid. The manual part I can figure out I just need someone to point me in the "
"direction to start."
""
#END
STR C0
OUT Y0

// Rung 2
// Address 2
#BEGIN COMMENT
"The Cmore will need to send four values for the hour and a value for the blowdown "
"duration to the PLC"
#END
STRE V7770 V2001
PD C1

// Rung 3
// Address 5
STRE V7770 V2002
PD C2

// Rung 4
// Address 8
STRE V7770 V2003
PD C3

// Rung 5
// Address 11
STRE V7770 V2004
PD C4

// Rung 6
// Address 14
#BEGIN COMMENT
"Is this blowdown control for top blowdown or bottom blowdown?"
""
"If it's for bottom blow then the value might be better expressed in tenths of seconds. "
""
"I find it hard to believe that you need bottom blows in the order of minutes per session "
""
"If you really need minutes then some PLC side math might be in order"
""
#END
STR C1
OR C2
OR C3
OR C4
STR C0
ANDN T0
ORSTR
OUT C0
TMR T0 V2000

// Rung 7
// Address 24
END

// Rung 8
// Address 25
NOP


#BEGIN ELEMENT_DOC
"Y0","","","blowdown valve"
"C0","","","duration seal in"
"C1","","","First blowdown time of the day OS "
"C2","","","second blowdown time of the day OS "
"C3","","","third blowdown time of the day OS "
"C4","","","Fourth blowdown time of the day OS "
"T0","","","duration sealin timer"
"V2000","hmi tenths","","tenths of seconds from HMI for blowdown"
"V2001","","","first hour# to blow down from HMI"
"V2002","","","second hour# to blow down from HMI"
"V2003","","","third hour# to blow down from HMI"
"V2004","","","Fourth hour# to blow down from HMI"
"V7770","","","Hours on the PLC clock"

#END
 
Works great

Milldrone I appreciate the help It works perfectly. It is a top blowdown there doing, one is a high pressure boiler and the other is a low pressure boiler. They want a seperate page for each boiler on the HMI so I will give them that and they should be good to go. Thanks again
 

Similar Topics

Is it correct to say that the dl05 program when uploaded does not store the current value in a v memory location? I have a customer that has one...
Replies
8
Views
3,069
Hello everyone, Background: We have a Directlogic 405 PLC that has an output card that has all solenoids on it. These solenoids are on plugs with...
Replies
9
Views
2,837
Can someone please explain the sinking and sourcing with respect to DL405 series PLC? I have already been through the manuals. Explanations with...
Replies
3
Views
1,969
I'm new to the whole Drum idea. I tried to figure it out but couldn't. I'm wanting to use a drum or sequencer to seqence a V memory depending on...
Replies
1
Views
1,443
any one know how to do PLC-to-PLC Communications over a network using two 205 DirectLOGIC PLCs. I can't even get the example given to work.
Replies
5
Views
2,598
Back
Top Bottom