Hi,
I have two identical RsLogix 5000, 1756-L61 PLCs connected to a Ethernet hub.
Slot[0] 1756-L61 Brain
Slo2[1] 1756-ENBT/A ENet
Slot[2] 1756-DNB DNET

I need to transfer tag data back and forth between these processors via Ethernet. I would like to use the MSG command but have no clue in some of the info I need to enter.
Can you give ma a idiot's guide to set this up?

Thanks ...
 
That is a big chapter - here's the short version.

Firstly I prefer to always read data from another PLC or controller, it allows for some traceability.

To read from another PLC, the communications path to the target must be specified in the MSG configuration dialog.

There are two ways to achieve this.....

a> "Build" the path to the target PLC in the I/O configuration.

Firstly add your own (Local) Ethernet module to your backplane (hint: right-click->New Module).
Fill in all the white boxes with the correct information.

Then add the remote EtherNet module to the EtherNet network that appears in the tree (Choose Comm Format "None").

Then add the remote controller onto the new "Backplane" that will appear in the I/O Configuration tree. The controller will then become a named choice for the MSG communication path.

OR:

b> Specify the path explicitly in the MSG configuration.

To do this, the path is made up of repeating pairs of data Port,Destination,Port,Destination etc..

Port : the Backplane port is number 1, "Front" ports are numbered sequentially 2,3,.... etc.

Destination : Either a Slot number, or an address....


Example :...

Assume
Local Controller, Slot 0
EtherNet Comms Module : Slot 1
Remote EtherNet Address : 192.168.4.67
Remote Controller : Slot 4

Path to the remote controller is then...

1,1,2,192.168.4.67,1,4

1,1 = Go out the back port to slot 1
2,192.168.4.67 = Go out the front port to ethernet address 192.168.4.67
1,4 = Go out the back port to slot 4


It has to be said the first method is preferable, as it helps to see the route of the comms.
 
Firstly I prefer to always read data from another PLC or controller, it allows for some traceability.

I used to agree with this - until I had a large network that was clogged up by the communications - The fix was to use event driven writes
i.e. don't send the message until the data has changed. This Reduced the network load 95% loading down to 15% loading

PS in Control logix I use the tag name for traceability eg Tag RX_PLC1 is a user defined data type DINT[60] that is received from PLC1 in PLC1 I use TX_PLC1
 
+1.
I don't see a need for messages especially when you can set up produced/consumed tags.

Agreed, but would you set up Produced/Consumed tags for data that only needs to be exchanged infrequently ? An example : passing a Recipe for the next PLC to process the batch, which might only need to be done every hour or so.

It would be overkill on network resource to use Produced/Consumed tags for this.

And don't forget that a P/C tag can only contain up to 500 bytes.

And don't forget that a P/C tag consumes a Connection. On a large system you may run short. A message can be set to relinquish its connection after the message is finished with, until the next time it triggers.

Each method has its merits - you choose the best method to fit the application.
 
Agreed, but would you set up Produced/Consumed tags for data that only needs to be exchanged infrequently ? An example : passing a Recipe for the next PLC to process the batch, which might only need to be done every hour or so.

It would be overkill on network resource to use Produced/Consumed tags for this.

And don't forget that a P/C tag can only contain up to 500 bytes.

And don't forget that a P/C tag consumes a Connection. On a large system you may run short. A message can be set to relinquish its connection after the message is finished with, until the next time it triggers.

Each method has its merits - you choose the best method to fit the application.
I agree on the recipe and such part.
But, as he stated he only has 2 CPU's thus connections/resources aren't an issue with his set up.
For a larger system/network I would investigate and decide.
 
I agree on the recipe and such part.
But, as he stated he only has 2 CPU's thus connections/resources aren't an issue with his set up.
For a larger system/network I would investigate and decide.

Isn't that what I said
Each method has its merits - you choose the best method to fit the application.
 

Similar Topics

Hi, If we have PLCs on different subnets is it possible to do TCP comms data transfer between them? I'm assuming if we use a routing switch and...
Replies
3
Views
819
Hello there, I'm trying to send the state of a single internal bit (B3:3/8) of my main ML1400 PLC to a different ML1400 over Ethernet using the...
Replies
4
Views
1,755
I need to get data from an MTS temposonics multi-magnet transducer to my motion controller. I think the best option, given the communications...
Replies
3
Views
1,830
Hi Guys, I am relatively new with the PLC's and even newer with A-B. I need to establish Ethernet communication between two controllers to...
Replies
3
Views
1,703
Hi all I have a problem with my thesis. I need to transfer data from Matlab to step 7, does anyone have solution for my case ? I use Step 7 with...
Replies
4
Views
5,666
Back
Top Bottom