V0N_hydro
Member
A number of our customers have been asking for historians recently. We normally use Citect or Wonderware for HMI and let that software take care of the data logging for trending purposes, but only keep 18 months data on the HMI platform.
I've never seen or used a historian. I imagine the historian doesn't have to come from the same vendor as the HMI, as the historian I think will retrieve the same data as the HMI via OPC or direct from the PLC. The Historian doesn't query the HMI datastore for the data. If communications are lost between the historian and the control system then no data is logged? Eg reboot the historian server and it doesn't have any records for the last 4 minutes?
Has anyone used or set up any historians which they would recommend? IEC 61850 would be a plus.
FYI we are looking at possibly 64 analog values to trend and another 500 trips/alarms/events that I imagine would be part of the history too.
For this small amount of data (albeit for very long time) I imagine today's 8-core 8GB ram servers would have no problem handing the load.
What happens when you need to replace the historian server hardware every 5 years?
Do customer IT departments handle the supply and care and feeding for the server or are control system suppliers also taking care of the IT side of Historians?
The historian seems to be a different animal than a control system with sensors, actuators, PLC and HMI.
Thanks for your thoughts
I've never seen or used a historian. I imagine the historian doesn't have to come from the same vendor as the HMI, as the historian I think will retrieve the same data as the HMI via OPC or direct from the PLC. The Historian doesn't query the HMI datastore for the data. If communications are lost between the historian and the control system then no data is logged? Eg reboot the historian server and it doesn't have any records for the last 4 minutes?
Has anyone used or set up any historians which they would recommend? IEC 61850 would be a plus.
FYI we are looking at possibly 64 analog values to trend and another 500 trips/alarms/events that I imagine would be part of the history too.
For this small amount of data (albeit for very long time) I imagine today's 8-core 8GB ram servers would have no problem handing the load.
What happens when you need to replace the historian server hardware every 5 years?
Do customer IT departments handle the supply and care and feeding for the server or are control system suppliers also taking care of the IT side of Historians?
The historian seems to be a different animal than a control system with sensors, actuators, PLC and HMI.
Thanks for your thoughts