I'm using FC105 Scaling block for analog periphery reading.Are there any reading difference of betweens voltage,current,resistor,thermocouple for scaling?
That is ;is it enough directly PIW using?.. Thanks in advance...
Siemens works with an input integer from 0 to 27648. This can correspond with 0 to 10V, 4 to 20mA, 0 to 20mA, depending on what your settings are in the hardware config.
More can be readed on the page KalleOlle has given.
The FC105 only does a simple math calculation.
It devides PIW by 27648 and then multiplies by your range and adds an offset.
Formula from Siemens manual:
OUT = [ ((FLOAT (IN) – K1)/(K2–K1)) * (HI_LIM–LO_LIM)] + LO_LIM