I have a chassis with 3 1756-CNB/D cards in it, about once every 2 or three weeks all 10 AB Powerflex 700 drives on this one card fault out, I go to the cabinet and the ok light on the front of the card is red and the following error message is scrolling across the display:
Assert:Null.C line 0445
I have done some surfing on the knowledgebase but no luck with this error.
Thanks in advance for any help
 
I have never seen that CNet error myself. However, if you want to at least find out if is the card itself, or the network, I'd swap the suspect card with one of the others in your rack. If the same drives fault out, then you know that your card is fine and that you have an issue with the media or one of the drives. If the new network faults, then you know that the card is bad.
 
I have never seen that CNet error myself. However, if you want to at least find out if is the card itself, or the network, I'd swap the suspect card with one of the others in your rack. If the same drives fault out, then you know that your card is fine and that you have an issue with the media or one of the drives. If the new network faults, then you know that the card is bad.

Thats an excellent place to start troubleshooting and if i havent nailed down a solid answer by this weekend i will give it a shot. Cant power down till then production runs 24/7
 
Definitely check the ControlNet modules (and the controller) for the "Atmel64" backplane ASIC chip issue. It sounds like a defective 1756-CNB component to me.
 
Definitely check the ControlNet modules (and the controller) for the "Atmel64" backplane ASIC chip issue. It sounds like a defective 1756-CNB component to me.

Thanks Ken
not sure exactly what a Atmel64 is? but i will dig into it.

also if it helps any,this system has been up and running and untouched (as far as i know) for about 5 years and this intermitten issue just started a few weeks ago.
 
Ken
does that have something to do with the way the controller interacts with the chassis backplane??
I found something similar on knowledgebase.
 
I should have been more specific; in the A-B world this was a well-known chip problem that affected a lot of controllers, network modules, and motion modules. There was a bad batch of backplane bridge chips, and the batch was from Atmel and had a batch number printed on the chip that ended in "64". Chips from Samsung and Phillips and Atmel chips that ended in 65 were not affected.

The issue was called ACIG 2007-05-002; you can search for that in the Knowledgebase or go directly to Articles 40149 and 41204.

Since your system has been running since before the bad production batch it might not be affected. Also, most of these failures appeared right away when the system was commissioned. But when you're dealing with a crash of the firmware in the 1756-CNB, you have to rule this issue out before proceeding.
 

Similar Topics

Good day and Merry Christmas Eve. The title's error has been dogging me for roughly a month and today I finally figured out what the issue was...
Replies
0
Views
2,274
Dear all I have an ALLEN BRADLEY PLC system with a local and a remote rack. On the local rack I have 1756-CN2 and on the remote rack I have...
Replies
2
Views
1,879
Hello all, I'm am trying to figure out how a message initiated from a controllogix processor writes to a SLC 5/04 using control net. Reading the...
Replies
2
Views
1,855
What's the difference between the two? What's the proper one to use for communicating to a remote i/o rack via controlnet (this is for a Control...
Replies
1
Views
2,626
Hello, Is there any issue in term of the firmware revision for all of these three devices to communicate with each other in one rack? I'm...
Replies
2
Views
4,262
Back
Top Bottom