It has been said in previous posts here that Pressure Control is typically an integrating process (non-self-regulating).
However I am having trouble wrapping my head around a particular setup.
I realize in the following ideal scenario (split range PID) that the pressure control process would be integrating, with a final control element that increases or decreases pressure in a vessel:
CV: < 50 % - Release pressure in the tank at a rate inversely proportional to the output.
CV = 50% - Idle, remain at current pressure.
CV > 50% - Increase pressure in tank at a rate proportional to the output.
However, let's say another vessel has a relief PCV that vents pressure in the tank: 100% is Open, 0% is closed, the valve merely vents the tank.
Additionally, there is a separate mass flow controller regulating the rate of air entering the tank.
Assuming the MFC is left at a constant rate of air into the tank, is the Pressure Control process now self-regulating (non-integrating)?
Let's say air is entering at a fixed rate of 300 SLPM.
PCV PID loops kicks in and eventually the valve reaches 25% open, steadying at a desired setpoint of 2 PSIG.
Setpoint now increases to 5 PSIG. PCV eventually starts to close and will now settle at a different CV to compensate.
Isn't this a self-regulating process?
However I am having trouble wrapping my head around a particular setup.
I realize in the following ideal scenario (split range PID) that the pressure control process would be integrating, with a final control element that increases or decreases pressure in a vessel:
CV: < 50 % - Release pressure in the tank at a rate inversely proportional to the output.
CV = 50% - Idle, remain at current pressure.
CV > 50% - Increase pressure in tank at a rate proportional to the output.
However, let's say another vessel has a relief PCV that vents pressure in the tank: 100% is Open, 0% is closed, the valve merely vents the tank.
Additionally, there is a separate mass flow controller regulating the rate of air entering the tank.
Assuming the MFC is left at a constant rate of air into the tank, is the Pressure Control process now self-regulating (non-integrating)?
Let's say air is entering at a fixed rate of 300 SLPM.
PCV PID loops kicks in and eventually the valve reaches 25% open, steadying at a desired setpoint of 2 PSIG.
Setpoint now increases to 5 PSIG. PCV eventually starts to close and will now settle at a different CV to compensate.
Isn't this a self-regulating process?