Micrologix 1500 AWA with ac prox. question

loundeb2

Member
Join Date
Jul 2010
Location
ny
Posts
111
Hi,
I have a ML1500 awa base plc that i'm wiring to a punch press. The press has notched steel wheel and an ac inductive proximity sensor for positioning and speed monitoring. My question is, could I use the HSC function to count the pulses of the sensor or will it only work for DC inputs/devices?
Thanks!
 
I am not sure what your results were, but I would have guessed that your inductive prox was too noisy for the application. You might have been able to sense the changing position but you probably didn't get the velocity. You do elude to an interesting question: is the amount of time for the inductive prox to generate the voltage level high enough to switch the switch on sufficient or would we need a faster acting DC device? Further would hysteresis of the prox cause problems? So did you try it?
 
But is a run of the mill general off-the-shelf DC inductive proximity switch responsive enough to adequately measure speed and position. My afore-stated argument is that it is not. (I missed that he stated that he has an ac prox, my statements assumed that he had a DC prox.)
 
Thanks for the input. The ac AWA 1500 does have two HSC function files available, although you can't adjust the filters. I did try an ac prox using HSC0, but it wouldn't react fast enough, thus counts were sporadic at best. Filtering would be necessary.
I did think about using a solid state relay to interface with the ac inputs of the AWA, but not being able to adjust the filters, I decided to go with an anti-tie-down program using the prox and timer.
 
Last edited:

Similar Topics

I have been working on this for a while now and I can't seem to get it. I was finally able to view the 1500 on the PanelView under the serial...
Replies
1
Views
79
Hello, I have a 1764 1500 LSP Series A that keeps failing with DTL_E_FAIL I/O error. Searching around it seems there's a weird issue specifically...
Replies
2
Views
103
Good Day i Have Micrologix 1500 LSP, and I want to get data from plc and send it through Modbus RTU slave; I have only ch0 on that plc I Order...
Replies
6
Views
917
Hello folks, Hope everyone is doing fine. I got an OMRON NS10-TVOOB-V2 hmi screen last day and planning to use it with Micrologix 1500. 1. Is...
Replies
4
Views
1,206
Good morning to all, I need to modify an existing PLC MIcrologix 1500 configured with a Modem on Channel 1 (DF1 Full Duplex) and an...
Replies
7
Views
1,425
Back
Top Bottom