1794-ASB to PLC-5/40e

cnorm5623

Member
Join Date
Sep 2010
Location
Kalispell, MT
Posts
26
Hi
we are trying to add a 1794-asb to a plc-5/40e and not having much luck. so far we are stuck when trying to auto config the rack in the plc-5. we get the error :make sure I/O Status file exists: but we have added the I/O status file in S:16 so not sure what is going on.

currently we are just trying to hook it up to our test lab to get it going. we are on channel 1B on the PLC 5. umm let me know what else ya need to know. we are having server problems right now so i cant access the program but soon as i can i will get more info
 
It would help someone help you if you could post your PLC program ( .RSP file) zip it first.
Also post the dip switch settings of your 1794-ASB. And modules connected to the ASB
( complete catalog numbers).

Proper termination resistors, both ends. Double check wiring.

You can automatically configure the scan list if programming online.

To automatically configure the scan list:

1 Make sure the processor is in remote program or program mode.
2 Make sure the I/O data tables are large enough to handle the configured addresses, as the auto configuration operation will not resize them.
3 Make sure you have defined an I/O status file.
4 Make sure you have accepted any edits you have made to the channel configuration.
5 Click Auto Config. The system polls the devices on the I/O network and configures the scan list. If some or all of the adapters are not shown on the scan list, make sure they are powered, that they are properly connected to the correct channel, and that their hardware settings are correct.

Note: Automatic configuration displays the actual hardware configuration, except for racks that have their global inhibit bit set. In this case, the global rack inhibit overrides the automatic configuration.

© 1997 Rockwell Software Inc.
 
Last edited:

Similar Topics

Greetings all first wanted to say thanks for all the great info as I have been looking here a lot trying to figure out my issue, but having said...
Replies
13
Views
4,759
Hello, a customer i support has DH+ RIO racks all over the plant. they use 1794-asb modules. today they had a rack fault out and go unresponsive...
Replies
0
Views
647
I'm experience issues on a linear pick and place machine. The drive is a AXIMON DV10 and the Controller is an AXIDYNE 9972443. The problem I'm...
Replies
4
Views
1,852
Hello all. I have a job to add a 1794-IE8 Card in slot 5 on an existing Flex IO Rack which uses a 1794-ASB communications module, which...
Replies
8
Views
2,988
Sorry to bother everyone but I'm having real problems. The setup is: SLC5/03 with a 1747-ASB series B in slot 1. 1794-ASB series E in the field...
Replies
14
Views
2,139
Back
Top Bottom