Hello. I bought a PLC with analog input(0..10V), and I need to measure temperature. Thermometers with this voltage output are expansive and i dont need the measurement to be much precise or linear. Does anyone have an idea how to solve it? Could I use perhaps a thermistor or something like that?
 
With this solution first check that the analogue input won't be damaged if it sees 24V, it never should see the full 24V but could if there is a fault with a resistor or the PT100 sensor. Now we come to the problem, for a PT100 sensor the maximum current to avoid self heating is 1mA, to limit the current to 1mA you need a loop resistance of R=V/I : 24/0.001 = 24000 ohms.

If you connect in series a 24000ohm resistor and a PT100 sensor you can measure the voltage across the sensor. The PT100 sensor has a resistance of 100 ohms at 0C and 138.5 ohms at 100C. Resistors in series share the voltage in proportion to their resistances. So with a 24V d.c. supply at 0C you have 100/24100 * 24V = 0.099V, at 100C you have 138.5/24385 * 24V = 0.137V. You get a 0.382V difference for a 100C change. It is unlikely that this will give you any kind of sensible result.

I would be looking at using a converter/transmitter like these:
http://cz.rsdelivers.com/product/lkmelectronic/lkm-214-3/transmitter-lkm-214-3/3707940.aspx

http://cz.rsdelivers.com/product/lkmelectronic/lkm-103-2/transmitter-lkm-103-2/3707748.aspx
 
Thank you for the advices, but these solution are more expensive than a new thermometer with output 0-10V. So it seem that it would be a good idea just to buy it.
 
brian it is 0.0385 volts difference as low is 0.1 volt and 100 is 0.1385 volts.
if you have 10 volts max it means 0.4 percent of full scale
i use only a XTR105 costing about 10 euro/piece it has linearization and needs no external power, just 24 volts and you will need a resistor of 250 ohms.
it will be very precise
if needed just ask and i will send you more info on it.
 
That sound good. The output of this homemade thermometer should be voltage(around 0-10V) (the analog input on the PLC is 0-10V). Send me please some more info about that.
 

Similar Topics

Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
Replies
9
Views
241
I have a SX2 plc and i'm getting 0-10v analog signal,but i need 10bar analog output in 0v can someone explain how its done
Replies
2
Views
532
We have a 4 wire 0-10V analog OPT2012 (Time of flight distance laser) from Wenglor that we're experimenting with. We are able to teach the laser...
Replies
3
Views
527
Hi All, Not strictly PLC, but I'm sure someone works with this stuff and might be able to point me in the right direction. I'm designing a...
Replies
11
Views
1,032
We have constructed a new vibrator control station with local pots on the panel and remote pots on a wireless system. We are running 6 AB 525...
Replies
5
Views
701
Back
Top Bottom