AB Analog Ouput Voltage problem

GTX

Member
Join Date
Dec 2003
Posts
36
Hey

I am trying to set up an analog output on my Micrologix 1500 PLC and i have it setup to do 0 - 10 volts. But when i measure the actual voltage coming out its only 3.2 volts.

Any ideas what I am missing in the setup to have this problem ?

Thanks for any help

Barry
 
I assume you have the channel enabled.

What data format do you have it set to?

What value are you writting to the output?

Do you have it wired for voltage & not current?

What have you selected the output range to be? (default is +/- 10V)

Have you checked the resistance between Vout and ANLG COM(power down first), should be 2K?

Darren
 
- I have the channel enabled
- I have the data set to Raw/Proportional
- I am trying to write a value of 10000 (10 volts) to the output
- I have it wired to the voltage not the current
- my selected output range is 0-10 volts

I will go check the resistance right now.

Thanks for your help :)

Barry
 
Every thing is working fine. A value of 10000 is exactly 3.204 Volts. If you want 10Vdc then use 31207. What it sounds like you really want is the data format set to Engineering Units (0-10000)

Raw/Proportional is:

0 -> 0Vdc
31207 -> 10Vdc

Darren
 
Last edited:
Darren,

THANK YOU SO MUCH !!!

I switched it to engineering units and everything works fine !!

Thanks for all your help,

Barry
 

Similar Topics

Hello all. I'm working with an Allen Bradley micro 850 PLC. I am configuring an analog output module to give me 0-10 V value to another PLC's...
Replies
3
Views
4,478
I have connected a sensor which gives 0 to 10V to a DVP 20EX PLC's analog input. According to the manual of the PLC, its ch0 analog input is at...
Replies
0
Views
2,896
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
Replies
5
Views
79
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
30
Views
1,086
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
246
Back
Top Bottom