Siemens Mobile panels 'freeze'

Plc_User

Member
Join Date
Dec 2005
Location
Belgium
Posts
317
I have 4 mobile panels 177 on a Profibus network, and somtimes a panel (not always the same) freezes (no manipulation is possible anymore).
In the software of the panel I have one tag that sees an integer variable in the plc that is raised with value one each scan cycle of the plc, this tag has an update time of 500 ms cyclic continuous.
This tag has an event on change of value that is transfers its own value to another tag.
This last tag has an update time of 500 ms cyclic continuous and the plc looks at this tag to see if the panel is connected (this is an alternative for the live bit of the panel, that I didn't wanted to use).
Could this be a reason for the freezing of the panel (no manipulations possible anymore)?
Or could there be other reasons?
As an alternative I tried to use the life bit of the coordination word from the area pointer of the panel.
This worked ok for one panel, but if I connect more then one panel I get a system message on the panel on startup : 'Interference on the bus'.
The area pointer for coordination for each panel in the cpu are in different databloks for each panel.
Why doesn't this work for more then one panel on the bus??????
 
Are the bus parameters calculated correctly ?
Do you have all 4 panels integrated in the same STEP7 project, and every other Profibus node as well ?

All 4 panels are integrated in the same S7-project (just as every node).
But I did not download the plc hardware since I added the panels.
Do you have experience with this kind of problem?
Since it are mobile panels, none of them can be connected, or all 4.
 
The TTR downloaded to all stations must be calculated by including all stations.

I have not experienced, but heard of panels behaving erratically when there are bus problems.
 
To come back on my second question :
///As an alternative I tried to use the life bit of the coordination word from the area pointer of the panel.
This worked ok for one panel, but if I connect more then one panel I get a system message on the panel on startup : 'Interference on the bus'.
The area pointer for coordination for each panel in the cpu are in different databloks for each panel.
Why doesn't this work for more then one panel on the bus??????
/////

Does anyone know how you set up the coordination area in multiple panels on a profibus network with one cpu?

Thanks
 

Similar Topics

Hello all, Just curious if anyone has experience with one of these panels, or the larger ones in the family of mobile panels? KTP700F, KTP900F...
Replies
7
Views
2,186
Hello, I have a project where I have 10 Diesel Engines running generators. Each of these engines have a Siemens 315-2 PN/DP plc in order to...
Replies
24
Views
10,810
Dear Every Body, We are seeking with a problem to upgrade the Siemens Make Mobile panel 170 by Mobile Panel 177. The system is running by...
Replies
0
Views
12,207
Hello All, I am hoping someone can help me out since I know Jack about Seimens PLCs. I have been given the task to figure out if a Siemens s7-200...
Replies
0
Views
4,603
Hi there! I have a production line which consists of several plcs and displays and machines. I want to use a Siemens mobile panel for manual...
Replies
2
Views
5,765
Back
Top Bottom