KalleOlson, those Siemens grounding recommendations are quite different from conventions in the rest of the control and drive world.
Hi Dick, 'quite different'? I don't follow you there...
Might be my fault,
I omitted their recommendations on the motor cables section, here it is:
4.2.1 Motor cables
⇒ Motor cables radiate a high degree of interference. In order to limit the emission level, shielded, low capacitance, 4-conductor motor cables should be used (U, V, W, PE conductors and outer shield). Suitable cables include, for example, SIEMENS PROTOFLEX. The cable shield must be connected at both ends to the housings/frame (ground) through the largest possible surface area. Cables with a YCY copper braiding provide a good shielding effect. They are better than cables with SY steel armor.
⇒ Feeder cables for motor temperature monitoring (PTC or KTY) must be routed separately away from the motor cables! We recommend that shielded signal cables are used.
⇒ If it is absolutely necessary to interrupt motor feeder cables to connect reactors or terminals, then the non-shielded cable should be kept as short as possible.
⇒ If it is absolutely necessary to interrupt the motor feeder cable to connect contactors, switches, terminals then these must be separately mounted away from other terminal strips, switches etc.
⇒ A suitable M gland with shield contact can be used to connect the cable shield to the motor. It must be ensured that there is a low-impedance connection between the motor terminal box and motor frame (ground).
⇒ The motor terminal boxes should be manufactured out of metal and be electrically conductive (gray cast iron / aluminum alloy). It must be ensured that the terminal box cover is flush with the terminal box so that there are no gaps which could result in an antenna effect.
Kalle