downloading problem with PV550

babuganesh

Member
Join Date
Mar 2011
Location
singapore
Posts
1
Dear all,

i have a upload and downloading problem with my Panelview 550. i cannot communicate the PV with the system. help me to download the file directly from the system to PV550.

panelview 550
cat no: 2711-A5B5
cable catalog no : 2711-NC13
 
Welcome to the forum babuganesh.

Do you mean 2711-B5A5 ? If so your PV supports DH485 protocol. The cable you have is correct ( a straight thru cable). If your PC/Laptop has a real serial port then use the 1747-PIC/AIC+ driver in RSLinx to get connected to the PV. If you don't have a real serial port you will need a 1747-UIC ( USB to DH485 converter).

What version of RSLinx do you have?

Do you have PanelBuilder32 software? You will need it also.

Another method to upload/download programs is the use of a memory card.
See PDF below for more info on that.
 
Last edited:

Similar Topics

Hello everybody, I have a problem with TwinCAT 3. When I try to activate a configuration and start IPC in Run mode I receive an error AdsWarning...
Replies
3
Views
5,618
Dear Friends Please I face problem with Simatic PLC S7-415H , I can go online throw IP/TCP network and uploading the logic from PLC too PC but...
Replies
2
Views
1,774
Hi guys!! Back again with another issue... Im currently working with Crimson 3 and a G315 HMI. While working on a database I previously...
Replies
3
Views
2,448
Hi All! I added a combination I/O module 1794 IE4 XOE2/B to the end of 1794 RIO devicenet node. In RSNetworx for Devicenet V11 (CPR9) for some...
Replies
5
Views
5,144
I have a Q00 PLC from a customer who want to modify some in Main program. First I upload program from PLC using GXWork 2. Everything is ok. But...
Replies
0
Views
4,406
Back
Top Bottom