Hello.

I have the following program using Micro 1000 to control a VFD (PF4).

My question is how can I use the Bin_Ret prox switch input (I:0/7) to stop the drive, instead of just sending back into forward. Then operator can push start PB again to restart cycle.

Thanks,

Robert
 
Last edited:
I haven't looked at the program yet, but in most VFD applications there are several VFD inputs available, usually programmable. The functions include run forward, run reverse, controlled stop, and "emergency" stop. If you look at the drive manual you should be able to identify the available inputs, program them accordingly, and use outputs of the PLC hardwired for control. If you have a comm link to the drive you can usually accomplish all of these functions that way as well.
 
Thanks for the reply.

Actually, if you see the program, you can see how I programmed the drive with the inputs I had.
I did some testing on it, and noticed I missed something.
What I ended up doing was put that prox as an XIO before all the scaled limits for VFD speed, and the rest of the MOV's work now, and the drive can be started and stopped (with different speeds) based on what the prox is seeing.

I'll post the updated program so you can see (into the original message).

Thanks again for the prompt reply.
 

Similar Topics

I have a Powerflex 700 and a 1.5 hp motor I've hooked up to my Micrologix 1500 and test box. I was trying different start/stop setups today, and...
Replies
8
Views
2,201
Hi all, New here and new all round to PLC`s. We have a servo drive that runs a cross travel beam backwards and forwards. I am having trouble with...
Replies
3
Views
194
Hi , Looking for some help. We have a 343-1 PN Lean Card & 315-2DP connected to an external system collecting data. After a recent shutdown...
Replies
0
Views
65
I have this 525 that i am controlling it via ethernet. I needed to jog the drive using a start PB. when the button is pressed, the drive moves and...
Replies
6
Views
670
We have several Powerflex 4M (22F-D013N114) VFD’s controlled by compactlogix PLC’s. Control is simple, a run and direction signal with the speed...
Replies
6
Views
1,523
Back
Top Bottom