Hi

I have set up 2 controllogix 13 slot chassis as follows:

Chassis 1 contains a 1756-L55 CPU and a CNB/D module (node 1) + various I/O modules.

Chassis 2 contains a CNB/D module (node 2) in slot 0 and various I/O modules.

I have connected the 2 CNB modules in the approved manner using controlnet taps, etc. and I have scheduled the network with RSNetworx for ControlNet. The I/O is responding without error.

Now to the question. The status displays cycle through the following messages:

CNB 1 shows OK, %C22, KpAv, nC01, nU05, A#01
CNB 2 shows OK, %C27, KpIv, nC11, nU00, A#02

What do these messages mean? I cannot find anything in the CNB user manual that describes these messages.

Thanks in advance

Keith
 
Really simple ! . It shows the CNB Status (OK ) CNB CPU Utilization (%C22 means 22 % ) KpAv ( i guess - Active Keeper ) , nC01 ( i think - no: of connections ), nU05 ( means network Update time or NUT = 5ms ) and adress A#01.

You can see all these things if you go to Module statitics of your CNB module through RSLinx. ( Right click on CNB in RSLinx and select statistics )
 
These diagnostic codes were added to the 1756-CNB in Series C, and I still don't have them memorized. They are better laid out in the Module Statistics that are accessible via RSLinx. That also includes some network-wide settings and some more statistics about errors and events.

You can also read them in the Release Notes for the module:
http://www.ab.com/manuals/cl/1756-rn587e-en-p.pdf


nC ## ## indicates the total number of open connections
Max = 64

nU ## ## indicates the total number of unconnected buffer usage
Max = 20

%C ## ## indicates the module’s CPU utilization percentage
Max = 99%

Bx ## ## indicates the number of bandwidth exceeded occurrences
since the last module reset
Max = 99
Note: This counter display is disabled until the module detects
at least one bandwidth exceeded event

Kp ## Keeper status

If ## equals: The module is:
Ov Offline with valid keeper information
Oi Offline with invalid keeper information
Av An active keeper
Ai An active Invalid keeper
Iv An inactive valid keeper
Ii An inactive invalid keeper
 

Similar Topics

Hey everyone, looking for advice in this particular scenario. Currently we have a controlnet bus that has (6) CN2DN devices and (2) powerflex...
Replies
5
Views
201
Does anyone know of a cheap USB to ControlNet or USB to DeviceNet adapter (I'm looking for both). I thought PLC Cable would have one but I did not...
Replies
16
Views
2,250
I'm having an issue trying to backup a ControlNet network. Within RSLogix5000, when I click on Module Properties of the 1756-CNB (Rev 5.001), the...
Replies
2
Views
853
An issue occurred at an organization here in whereby the ControlNet card developed a fault. Card Details: Catalog/Series; 1756-CN2RXT B Part No...
Replies
0
Views
434
Hi, We have ControlLogix installed at my plant with Flex IOs communicating with controller through ControlNet module. Yesterday, while controller...
Replies
0
Views
484
Back
Top Bottom