setting up vac/pressure x-mitter

swaneyj

Member
Join Date
Jun 2008
Location
SouthCarolina
Posts
44
I have a foxboro transmitter that is set up now for pressure. I am changing it to a vac/ press. The range on the transmitter now is 0-60 psig. My min and max is 0-600 (hex/bcd). My new range will be -14.7 psig - 100psig. I am reading this on a HMI and not sure how to range my plc or hmi. Any help?
 
1794-if4i

I was afraid of that. Your card can be configured for different raw data values depending on the input to the card. Can you tell us what electrical input you are using ( 0-10v , 1-5v , 4-20ma) And also how is the card configured ( see PDF below for more on this.

If ( big if) you have a 4-20ma input and the card is configured for 0-30840 raw data. Then see sample scaled program below for how to scale your input to -14.7 to 100.

If the card is configured differently then lets us know and we can revise the program.

scaledvalue.jpg
 

Attachments

  • inputconfig.pdf
    57 KB · Views: 6
Looks like it is scaled 0-2048 in decimal and if you look at it in BCD format it is 800. Which in turn is 80 psig range of the transmitter now. Could I do what you guy's were talking about any way?
 
Last edited:
Not sure if I have the time to send it right now got a hundred things going on at one time. I will try. As you can tell I pop in and check messages when I can.

As far as the BCD I just go to the Change radix to look at it.

But the way you said might work.
 
The card you gave us 1794-IF4I is only a 4 channel input card. The program you posted
would be for a card with at least 16 channels. Are you sure about the card's catalog number ? It makes a big difference on how it's configured.

Is rack three a flex I/O or a 1771-ASB ? It looks like the module could be a 1771-IFE/ A , B or C. Please verify this it would make a big difference in how you scale for engineering units as the raw data will be a different value.

I think we are getting closer to a solution.
 
Last edited:

Similar Topics

Good morning fellow sea captains and wizards, I am being asked to do the above and obtain 4 values from each slave, I know about the MRX and MWX...
Replies
27
Views
589
SELECTED NEW FILE SELECTED PROCESSOR TYPE SELECTED I/O CONFIGURATIONS IM UNABLE TO CONFIGURE MY I/O’S. I HAVE A PAPER COPY OF A PROGRAM AND I...
Replies
0
Views
80
Does Rockwell still offer reset codes for old school Master Disk floppy's? In a bind and need to reset the activation disk soon and to be pointed...
Replies
9
Views
229
Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
76
Hello. I am trying to use a Prosoft AN-X4 to improve the communications for a new panelview plus 7. This is going from a SLC-500 through DH+ to a...
Replies
9
Views
282
Back
Top Bottom