Analog input module

BoTJe_84

Member
Join Date
Apr 2011
Location
Amsterdam
Posts
6
Hello,

I have a sm 331 analog Siemens module and i'm having trouble wiring it up.

The manual tells me to wire it like "picture 1".

But i thought it had to be like "picture 2".

A few facts :

- Siemens S7 331 7KF02 0AB0 module
- I want to have a 4-20mA signal
- The sensor is an LDR in combination with a ressistor (value = 1200 - 6000 ohms)


When I configure it like picture 1, i don't get anything in my VAT.

When I configure it like picture 2, i get a signal but it's only 0,2 mA. When i measure it without the plc (just 24VDC + LDR + resitor) i get a 4 - 20mA signal.

Are there any hardware or software adjustments that i have to do?

Thanks in advance !

Picture 1 :

Keuze_2.jpg



Picture 2 :

Keuze_3.jpg
 
On the side or back of your card there is a resistor brick that has to be taken out and put into the right position (matching arrows). The position must correspond with that in the HWManager, and match 20mA measurement. There are 2 types of 4-20mA measurements; loop powered (picture 2) and externally powered. Your card might be configurable to power the loop as in picture 1, check in the HWManager.


With a grain of salt (not having the gear here)

Kalle
 
When i wire up the analog module i get a SF red led.

Connections :

- 1 (L+) = 24VDC
- 11 (Mana) = 0VDC
- 20 (M) = 0VDC

When I select Volt choice in HW config, i have no fault
When I select Deactiviated in HW config, i have no fault
When I select Current (2 or 4 wire connect) in HW config, i have a fault

Anyone know what i do wrong?
 
When i wire up the analog module i get a SF red led.

Connections :

- 1 (L+) = 24VDC
- 11 (Mana) = 0VDC
- 20 (M) = 0VDC

When I select Volt choice in HW config, i have no fault
When I select Deactiviated in HW config, i have no fault
When I select Current (2 or 4 wire connect) in HW config, i have a fault

Anyone know what i do wrong?

In HWmanager; did you uncheck for 'Wire Break'? (Assuming that all mA inputs are not connected.)

Kalle
 

Similar Topics

Why AMIo800 Analog input module's I/O LED is Lighting up Red? Checked module connections, 4-20ma wires etc but this light is continuously Lighting...
Replies
1
Views
112
In this sample programming, what does U4 mean? Any assistance would be greatly appreciated.
Replies
8
Views
273
Dear Members; We have Fluke 754 hart communicator. We have wired up three transmitters of Rosemount Model C3051 with this input module. But when...
Replies
4
Views
1,848
Hello all, Thanks for the forum which has provided me with a lot of help overtime. I'm posting my first thread since I can't seem to find an...
Replies
4
Views
2,034
I am facing an issue module 1756-OF8 is showing the minor fault = recoverable in the module info.How can i reset it?
Replies
0
Views
1,759
Back
Top Bottom