ndzied1
Lifetime Supporting Member
Hi All,
We have a customer that has a system with several 24V power supplies in it. This has always worked fine when powered from the grid.
They now have an installation that is fed from a generator. Each enclosure (6 in all) has a starter for a single phase 2 HP 240VAC motor as well as the 24V system.
When more than 3 of these 6 units are turned on, the 24V systems drop out and lose communication with the master controller. This only happens on generator power, not on grid power. Adjusting the generator voltage up a bit seems to
actually make it worse. To make matters worse, the motors are starting under load. They drive a very, very small hydraulic pump that has to come up to pressure before I can shift the valve and start the cylinders moving.
We tried to put a surge suppressor (not believing it would really work) in the system but to no avail. It did not seem to have any affect at all.
Does anyone have any experience or success in applying 24VDC power supplies in generator systems? The specific power supply we are using in this case is found here:
http://eshop.phoenixcontact.com/phoenix/treeViewClick.do?UID=2866611&parentUID=&reloadFrame=true
Note, the generator is at least twice as large as it needs to be for the motor loads.
Thanks
We have a customer that has a system with several 24V power supplies in it. This has always worked fine when powered from the grid.
They now have an installation that is fed from a generator. Each enclosure (6 in all) has a starter for a single phase 2 HP 240VAC motor as well as the 24V system.
When more than 3 of these 6 units are turned on, the 24V systems drop out and lose communication with the master controller. This only happens on generator power, not on grid power. Adjusting the generator voltage up a bit seems to
actually make it worse. To make matters worse, the motors are starting under load. They drive a very, very small hydraulic pump that has to come up to pressure before I can shift the valve and start the cylinders moving.
We tried to put a surge suppressor (not believing it would really work) in the system but to no avail. It did not seem to have any affect at all.
Does anyone have any experience or success in applying 24VDC power supplies in generator systems? The specific power supply we are using in this case is found here:
http://eshop.phoenixcontact.com/phoenix/treeViewClick.do?UID=2866611&parentUID=&reloadFrame=true
Note, the generator is at least twice as large as it needs to be for the motor loads.
Thanks
Last edited: