Bit Memory adressing limit for Siemens CPU

userxyz

Member
Join Date
May 2002
Location
any
Posts
2,768
How can I know the bit memory adressing limit of a CPU ?

I have this CPU: 6ES7 314-6CG03-0AB0

M600.0 gives errors, not in PLCSim, only when downloading. When I change the adress to M100.0, no errors.

I googled for the resources of such CPU. But didn't find anything specifically about the adress limit...

Anyone know where to find this ?

Thanks,

Kind regards,
Combo
 
It is in manual.

For example, CPU314:


Data areas and their retentivity
Bit memory
Number, max. 256 bytes
Retentivity, available Yes (MB 0 to MB 255)
Retentivity, default MB0 to MB15
Clock memories 8 (1 memory byte)
 
it is given in the manual of the CPU or you can find it online in "Module information" of the CPU. No of Inputs, Outputs, Bit memory, DB memory timers/counters etc..
 
The editor does not check which CPU you are using. It is only when you attempt to download to the CPU that you will discover if any addressing is out of range for that CPU.
 
Module information...
Thanks, I'll check it out with an online connection tommorow.

Did you even open up the manual? For example CPU315-2DP has 2048 bytes of m area. Ofc editor must accept values like m300.0. Its the compiling state when you make the download that checks compability.

Imho, m area should be avoided when writing program.
 
ok

Yes I did. 314 has 256 byte's and 313 128 byte's.
But offcourse, DB's are retentive by default in simatic manager, m area is for testing. A collegue of me used the PLCSim and M600.0. This worked, but not in his CPU. When he changed it to M300.0 he could download and it worked...


Did you even open up the manual? For example CPU315-2DP has 2048 bytes of m area. Ofc editor must accept values like m300.0. Its the compiling state when you make the download that checks compability.

Imho, m area should be avoided when writing program.
 

I think DB's are easier to maintain and can be used with more describing symbols and structure. As with all, its not black and white never use m area, its more like use it only when really needed. Testing is one good use of it.

So back at you, why you would use m area over db?
 
Yes I did. 314 has 256 byte's and 313 128 byte's.
But offcourse, DB's are retentive by default in simatic manager, m area is for testing. A collegue of me used the PLCSim and M600.0. This worked, but not in his CPU. When he changed it to M300.0 he could download and it worked...

Yeah, plcsim sucks for many things. Never assume it works like real plc ;) for example some instructions clear accu2 when executed in plcsim but work like documented in real plc (ofc).
 

Similar Topics

Hi all , Thanks for this forum so far I got support from this forum . In rs logix 500 program B3:30/0, B3:30/1 internal memory bits used . I...
Replies
1
Views
2,067
Hello, First off, I would like to apologize for beginner question. I am looking to use a 'memory bit' to keep track of the status of an object...
Replies
2
Views
1,289
I have an Mitsubishi fx-2n-48-mrds. I noticed that some of the memory bits seem to act funny. Some of the latched ones do not stay latched and...
Replies
1
Views
1,940
Question for the Siemens experts. In an S7 safety function block, I'm adding two safety function blocks for emergency stops (F_ESTOP1, FB215)...
Replies
3
Views
4,936
New to PLC, I am currently doing a project on unity pro.? I want to indicate Circuit breaker closed status after the breaker...
Replies
3
Views
1,599
Back