configuring topic for compact logix in rslinx

eababio

Member
Join Date
Jan 2011
Location
Gaborone
Posts
52
Hi,
can anybody help with the proper configuration of a opc topic for compact logix 1769 l35E. I have tried but cannot get data using the OPC client even though the plc is connected in rslinx and can be seen as active in RSWho.I am using ethernet.
 
first things first ...

look at the Title Bar (usually blue) at the very top of your RSLinx window ... does it say "Lite" anywhere in the title? ... if it DOES, then you can't use DDE or OPC with that "free" version ... specifically, RSLinx Lite can NOT do DDE or OPC (even if the software will "appear" to let you set it up) ...

next thing, how are you trying to "get the data" from RSLinx? ... tell us what software package you're using - and how it's set up ... the more details you give us, the more helpful we can be ...

but ... as a simple answer to your question, usually you just click DDE/OPC on the RSLinx menu - navigate to highlight the PLC of your choice, then click "New" and give the topic an acceptable name - then click "Done" - and that USUALLY does it ...

dde_topic.JPG
 
Last edited:
I am using rslinx classic and compact logix . Hmi is IFIx and OPCpowertool as the opc server. The funny thing is it had worked until i changed IP adresses of both compact logix and the PC. Rslinx still connects and i can use rslogix 5000 but cant get the data through even the rslinx opc client.
 
personally I'd try deleting the existing topic - and then reworking it from scratch ... if I understand your setup, that SHOULD reset the IP addresses that are involved ...
 
As a note for anyone else that follows this thread in the future, you can also create a topic from the RSWho window. However, to edit or delete (and create) topics, Ron' tips above are the way to do it.

Browse to the controller you wish to communicate with and then right-click and select Configure New DDE/OPC Topic.

OG

OPC Topic.png
 
Last edited:

Similar Topics

Hello all and happy Friday, I'm curious if anyone here has experience sending data over an Anybus Bolt II (HMS AWB6001-A) using a Compact Logix...
Replies
4
Views
765
Hello everyone, I am looking for an easier way to configure all my IO for an OPTO22 PLC. I am developing in Codesys I have a GRV-EPIC-PR1 with a...
Replies
0
Views
585
Greetings to all. We have SST-SR4-CLX-RLL (Molex Modbus module) in remote backplane. The remote backplane, containing SST-SR4-CLX-RLL module, is...
Replies
0
Views
651
disclaimer- 1,no one in their right mind would pick this configuration but I want to try and get it working. 2, my MB knowledge is sketchy at...
Replies
5
Views
1,135
When configuring redundant ethernet cards, will the mac address change along with the IP address. A friend is having problems with IP security...
Replies
3
Views
1,256
Back
Top Bottom