showshocka Member Join Date Mar 2011 Location USA Posts 510 Apr 30, 2011 #1 Hi Guys...Good question here... I would like to turn "cooling 1 set point" off or bypass it. can i acommplish that by setting the source to Zero in the MOV instrution? would that be the same as a bypass? only troubleshooting.....
Hi Guys...Good question here... I would like to turn "cooling 1 set point" off or bypass it. can i acommplish that by setting the source to Zero in the MOV instrution? would that be the same as a bypass? only troubleshooting.....
bernie_carlton Lifetime Supporting Member + Moderator Join Date Apr 2002 Location Yakima, Washington Posts 6,413 Apr 30, 2011 #2 Probably not. The PID control would then try to 'cool' to a setting of '0'. It wouldn't 'turn off' the cooling.
Probably not. The PID control would then try to 'cool' to a setting of '0'. It wouldn't 'turn off' the cooling.
showshocka Member OP Join Date Mar 2011 Location USA Posts 510 May 2, 2011 #3 Basically I will have to find the cooling control for that rung and set the presets off for that MOV maybe like a Troubleshooting bit.
Basically I will have to find the cooling control for that rung and set the presets off for that MOV maybe like a Troubleshooting bit.
bernie_carlton Lifetime Supporting Member + Moderator Join Date Apr 2002 Location Yakima, Washington Posts 6,413 May 2, 2011 #4 Are you trying to turn off the cooling output? Do you want to control it manually? It's not clear.
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 May 2, 2011 #5 Put the PID loop in manual and move a value into the output 0 or 100% whatever direction stops the cooling process. If I understand you correctly.
Put the PID loop in manual and move a value into the output 0 or 100% whatever direction stops the cooling process. If I understand you correctly.
showshocka Member OP Join Date Mar 2011 Location USA Posts 510 May 2, 2011 #6 Thanks. Come to find out the operators put can toggle it at the speer panels.
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 May 2, 2011 #7 showshocka said: Thanks. Come to find out the operators put can toggle it at the speer panels. Click to expand... Toggle what? Just curious.
showshocka said: Thanks. Come to find out the operators put can toggle it at the speer panels. Click to expand... Toggle what? Just curious.
bornwild Member B Join Date May 2010 Location Riyadh Posts 429 May 2, 2011 #8 Just do it manually .Set the output to 0. Thats all,
showshocka Member OP Join Date Mar 2011 Location USA Posts 510 May 11, 2011 #9 Mickey said: Toggle what? Just curious. Click to expand... ok sure... toggle the cooling group 1 on and off from the speer panel..
Mickey said: Toggle what? Just curious. Click to expand... ok sure... toggle the cooling group 1 on and off from the speer panel..