module information s7 300

harrydeharry

Member
Join Date
May 2008
Location
Delhi
Posts
237
S7 gurus please have a look on the picture, every thing is working fine I had a doubt that is the memory condition is fine at the current PLC. or I should work more to remove the unwanted codes or reduce the code size.
Thanks in advance
Harry

module information.JPG
 
Hello Harry;
What results do you get when using the "Compress" button that you show on the left side of the screencapture you attached?
If you cannot free used memory that way, yes you will have to work on optimizing your code.
Hope this helps,
Daniel chartier
 
if i remember correctly, the memory on the 318 can be expanded by using a bigger plug in card
I dont think so.
The Work Memory is fixed. And since work memory is utilised 93%/90%, the CPU is practically at the end.

I think that the RAM Load Memory is used when doing online programming. So that is filled up now means you cannot do any further editing before you store the changes on the Memory Card.
 
thanks for all the comments and help.
Yes Mr. Jesper you are right when I downloaded all the program into mamery card all is under control.
thanks.
harry
 

Similar Topics

I have been given code to put in a machine. I didn't write the code and there is quite a bit in german and STL which I'm not very comfortable with...
Replies
3
Views
10,669
hi we have CP341(6ES7 341-1CH01-0AE0)modbus master and CPU414H in my site and i write FB (used FB8 & FB7) and DB for CP341 then download to cpu ...
Replies
1
Views
5,186
Hi Everyone, i was hoping for a little help with this module. i have data that needs to be read from a different plc through the Modbus plus...
Replies
8
Views
71
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
Replies
5
Views
89
Why does the controllogix redundancy modules use a single mode fiber vs multimode fiber?
Replies
1
Views
78
Back
Top Bottom