Hi,
I have a retrofit enhancement on an existing PV1000 (Not PV +).
It is a 2711-T10C10 with a RS232 port and DeviceNET.
I need to send a string out the RS232 port to communicate with a 3rd party machine.
The requirements are as follows:
Port Settings for the interface:
- 9600 baud
- 8 data bits
- 1 stop bit
- No parity
- No flow control
The data required would be RS232 standard control / data characters. Data would be 10 characters followed by a End of Line (Carriage Return) character.
For example I would need to send to the port: 0123456789<CR>
Any clues on if I can do this with the existing PV1000? If not, then what HW would you choose to upgrade with to achieve this? (Need to stick with Allen Bradley and Devicenet and minimum screen of 10" touch)
Thanks in advance
I have a retrofit enhancement on an existing PV1000 (Not PV +).
It is a 2711-T10C10 with a RS232 port and DeviceNET.
I need to send a string out the RS232 port to communicate with a 3rd party machine.
The requirements are as follows:
Port Settings for the interface:
- 9600 baud
- 8 data bits
- 1 stop bit
- No parity
- No flow control
The data required would be RS232 standard control / data characters. Data would be 10 characters followed by a End of Line (Carriage Return) character.
For example I would need to send to the port: 0123456789<CR>
Any clues on if I can do this with the existing PV1000? If not, then what HW would you choose to upgrade with to achieve this? (Need to stick with Allen Bradley and Devicenet and minimum screen of 10" touch)