Got a question, and hopefully I will get an answer.
I have a Redundant L61 with EN2T, CN2 and a RM module in a 7 slot chassis, and of course there is another one just like it, right next to it.

I have a L32E processor with built in ethernet port.

I want to produce and consume tags but its been so long since I have done this(controllogix only). I can't remember how this is suppose to be setup.

Is there a manual I can look over.

Thanks,
 
Since you have the 1756-RM, you can run version 19.52 of the Enhanced ControlLogix Redundancy firmware, which does support both I/O and Produced/Consumed Messaging over EtherNet/IP.

Chapter 7 in the "EtherNet/IP Modules in RSLogix 5000 Control Systems" manual (Publication ENET-UM001) is dedicated to Produced/Consumed Tags.

The Release Notes for version 19.52 Enhanced Redundancy specifically address the firmware you'll need in the CompactLogix for a reliable connection to be created and maintained over EtherNet/IP to the redundant ControlLogix. That's on Page 17 of those Release Notes, Publication 1756-RN684A.
 

Similar Topics

Hello, Have anyone here use Ignition to connect to a Remote IO using MQTT, then use ControlLogix or CompactLogix to connect to Ignition using...
Replies
1
Views
436
Im new to Ethernet/IP so I expected some issues but I am not sure if what I am trying to do is even possible. I believe these 2 PLCs should be...
Replies
6
Views
1,755
Hello! I'm struggling communicating a L320ER PLC through MSG Instructions, specifically I'm struggling with communication paths, I tried...
Replies
5
Views
1,328
I've been looking at some of the upcoming jobs we're doing where I work, and I feel like the scale would justify a ControlLogix instead of the...
Replies
11
Views
4,597
Client's Customer has an L64 v20 with MCI56-MCM Modbus in 2 slots. Client has an 1769-L16ER-BB1B v20 that needs to communicate with the L64 via...
Replies
3
Views
2,281
Back
Top Bottom