Hi all. Been surfing here since the site was recommended to me durring a Redlion sales call.

I am looking for a best practice on how to have a Redlion G15 report on the communications link to a Schnieder Momentum or Compact plc.

For monitoring the comm link between the plcs I use basic logic like this:

I transfer a register (ie 40001) with a value of one(1) to a second plc register (40002). the second plc has reg 40002 set at default to 0. When it recieves the value from the 1st plc it changes it to a 1 until the link is broken and the value of 40002 reverts to 0.

I was hoping that a data tag in the redlion would be able to have a default value set and when the the communications to the plc is lost the redlion would revert to that value.

I hope i did not miss it. If i did please someone point me in the right direction, if not this may be a good addition the Crimson 3.0 (wink wink).

Thanks,
Dennis
 
Hi all. Been surfing here since the site was recommended to me durring a Redlion sales call.

I am looking for a best practice on how to have a Redlion G15 report on the communications link to a Schnieder Momentum or Compact plc.

For monitoring the comm link between the plcs I use basic logic like this:

I transfer a register (ie 40001) with a value of one(1) to a second plc register (40002). the second plc has reg 40002 set at default to 0. When it recieves the value from the 1st plc it changes it to a 1 until the link is broken and the value of 40002 reverts to 0.

I was hoping that a data tag in the redlion would be able to have a default value set and when the the communications to the plc is lost the redlion would revert to that value.

I hope i did not miss it. If i did please someone point me in the right direction, if not this may be a good addition the Crimson 3.0 (wink wink).

Thanks,
Dennis

If all you want to do is determine if communications are active, use IsDeviceOnline(CPU1) replacing CPU1 with the name of your device. It will be 0 when the G3xx isn't communicating and 1 when it is.
 
JHarbin, I can not believe it was that simple. I have read the Crimson manual several times. Once you provided the answer I had to figure out where you got it from. Completely overlooked the Refernce manual. Thank you once again.
 
I typically set up a tag for each device called STATUS_COMMS and set its data =IsDeviceOnline(n) where n is the device number or name. Then you can easily set alarm triggers for the tag.
 

Similar Topics

Anyone, On how to configure Intouch to show server_fail pop-up from the SysPulse from InSQL. How to write a script for that and develop tags...
Replies
2
Views
2,210
We have a quad monitor setup with FT SE and we are utilizing a header screen at the top of every display. when we open a new page we abort the...
Replies
0
Views
92
Our plant manger/my boss wants each line to display the takt time above the line. I am trying to research the cheapest way to do this. Our plant...
Replies
3
Views
185
Hi Folks, Looking for support and ideas. We are trying to go online to monitor/fault find on an S7-300 programmed with TIA Portal V15. I can...
Replies
9
Views
347
We finally replaced our Cognex Checker with an IV-3 and I'm wondering if can replace the s/w in the monitor with anything else. I haven't been...
Replies
0
Views
100
Back
Top Bottom