ScottTheEngineer
Member
Hello,
The Facts:
1. I need to add a 1794-IB16 to a controlnet 1794-ACN15 module. The module currently has only an analog input card 1794-OE4 connected.
2. I have a laptop with the correct software (RSNetworx for controlnet) but no PCC slot to connect a PCD card. (also no PCD card)
3. Their is only one PLC on the Network. That PLC is a PLC5/80C with an Ethernet sidecar.
4. Is passthru availble
5. The data table for inputs on Node 5 (1794-ACN w/ OE4)shows 8 words.
6. Shutting down the processor or going to program mode will drop power to the entire plant. I can do it but it has to be brief and scheduled to prevent equipment damage. Zero tolerance for errors.
Questions:
1. If required, how do you write the new data to the 1794-ACN15 module without a PCD card or the KTC module which won't fit in a laptop either.(Haven't tried the hammer method though) and Will downloading to the ACN module fault the processor?
2. Will clipping the IB16 fault the processor? (thereby shutting the power off to the facility)
3. If I make the edit to the Controlnet offline, save the .XI file then integrate with the PLC5 through the controller properties page in RSlogix5 then clip the IB16 to the ACN module and download that to the plc5 will the I/O be available for use?
4. I tried several manuals but they don't really cover adding I/O to existing nodes (that I've found) only adding new nodes and I don't need that. Any manual recommendations?(please don't ask to me search AB's website I only have a few days)
The Facts:
1. I need to add a 1794-IB16 to a controlnet 1794-ACN15 module. The module currently has only an analog input card 1794-OE4 connected.
2. I have a laptop with the correct software (RSNetworx for controlnet) but no PCC slot to connect a PCD card. (also no PCD card)
3. Their is only one PLC on the Network. That PLC is a PLC5/80C with an Ethernet sidecar.
4. Is passthru availble
5. The data table for inputs on Node 5 (1794-ACN w/ OE4)shows 8 words.
6. Shutting down the processor or going to program mode will drop power to the entire plant. I can do it but it has to be brief and scheduled to prevent equipment damage. Zero tolerance for errors.
Questions:
1. If required, how do you write the new data to the 1794-ACN15 module without a PCD card or the KTC module which won't fit in a laptop either.(Haven't tried the hammer method though) and Will downloading to the ACN module fault the processor?
2. Will clipping the IB16 fault the processor? (thereby shutting the power off to the facility)
3. If I make the edit to the Controlnet offline, save the .XI file then integrate with the PLC5 through the controller properties page in RSlogix5 then clip the IB16 to the ACN module and download that to the plc5 will the I/O be available for use?
4. I tried several manuals but they don't really cover adding I/O to existing nodes (that I've found) only adding new nodes and I don't need that. Any manual recommendations?(please don't ask to me search AB's website I only have a few days)