OK seen this one.
5/03, I have burnt (charred) two processors I am hooked to a PV600 on DH485 on the RJ11 port. Replaced P/S Back Plane and processor at different times, I am thinking one infected another and now am waiting on New components, to replace them all, has anyone seen this, I HAVE NEVER IN MY 20+ YEARS:cry:
 
this might not be even remotely connected with your problem so don't let it send you on a wild goose chase ...

but ...

you need to be aware that two of the contacts in your processor's DH-485 port are used to supply 24VDC and a DC return to "other" devices which might be connected there ...

in other words, there's HOT STUFF and a RETURN PATH in that plug ... I've heard horror stories of bad things happening when the cable hooked into that port wasn't treated with respect ...
 
What's the history ? Were these systems just working and then went Pfft, or are they being hooked up for the first time ?

The only cable that should be used to connect a DH485-equipped PanelView Standard terminal to an SLC-5/03 Channel 1 DH485 port is a 1747-C10 or -C20.

These cables have a flat "AMP" connector on the PanelView side, and a RJ45 connector on the SLC-5/0x side.

post-7072-1204033960.gif


The RJ45 style plug on the PanelView itself is for connecting a 1747-PIC or 1747-UIC. It doesn't have the hot 24V pin.

That hot pin on the SLC-5/0x DH485 port has burt more than one Ethernet port up in the past when folks just assumed that any two devices with RJ45 connectors could be connected together.
 

Similar Topics

I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
81
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
Replies
2
Views
93
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
103
I have a redundant ControlLogix being set up. This program reads a value from a remote site which happens to be SLC PLC. Rockwell mentions SLC...
Replies
2
Views
95
Hello, I have a ControlLogix redundant controller being set up. The program reads a value from a remote site which hosts a SLC PLC. Rockwell...
Replies
0
Views
77
Back
Top Bottom