Hello all,

I have a micrologix 1400 with 3 expansion modules, an Analog Input (1762-IF4), a relay output (1762-OW8)and an Analog Output (1762-OF4).

I can only hook two modules at a time...whenever I hook up the third module, the PLC FAULT light and POWER light flash intermittently for about 1sec....the ethernet network lights also flash for about 1 second intermittently....the plc never boots up

I can mix and match the modules, but only two work..never three....so nothing seem to be wrong with the modules themselves...

Only other thing to note, is that I have these hooked up on a desk, for programming, not on a DIN rail...so maybe grounding is a problem?

any idea what is wrong?

thanks,
Ian
 
Ok, I just realized something..

The Analog Output Module works SOMETIMES....the other two modules work all of the time, so I guess the problem is with the Analog output module...

I checked on the bus terminator, but I don't see anything like that for the micrologix 1400..good suggestion though! thanks.
 
I checked on the bus terminator, but I don't see anything like that for the micrologix 1400..good suggestion though! thanks.

Sorry, I should have checked. I am used to the 1500. According to AB, the 1762 I/O doesn't require an End Cap with the 1100/1200/1400.

Stu....
 
What is a bus terminator?

I see references to a "bus terminator" for 1762 I/O modules for the Micrologix 1400.
I am doing a project using a ML 1400 and just added an -OW8: relay output module.
Do I need some other component called a "bus terminator" ? I know some systems needs end-of-line resistors for impedance terminations. Is this the case here?
 
I see references to a "bus terminator" for 1762 I/O modules for the Micrologix 1400.
I am doing a project using a ML 1400 and just added an -OW8: relay output module.
Do I need some other component called a "bus terminator" ? I know some systems needs end-of-line resistors for impedance terminations. Is this the case here?

No you don't need a bus terminator for the 1400.
 

Similar Topics

Hey all, first time poster here. I am wondering if anyone has tried using a Keyence SR-X300 barcode scanner to a Micrologix 1400. Keyence sent...
Replies
0
Views
12
I'm using a SLC typed write from the ControlLogix5572 to the MicroLogix 1400, with path: 2, (MicroLogix IP). The ControlLogix equipment has a...
Replies
0
Views
87
Hi, I am working with a Micrologix 1400 model 1766-L32BXB. With no input wires connected to the “in12” thru “in19”, I am getting 24 volts while...
Replies
4
Views
221
Hi everyone, I hope I don't butcher this up, please feel free to critique me wherever if I do, I have an issue I would equate to "chasing...
Replies
4
Views
300
Hi everyone, I'm working on a project where I need to exchange data between a Siemens S7-1200 PLC and an Allen-Bradley MicroLogix 1400 PLC. The...
Replies
8
Views
640
Back
Top Bottom