Hello again!

I have a little question for you guys.
I want to link two S7-300 controllers via Profibus (Master - CPU 313C via CP 342-5, Slave - CPU 317-2 PN/DP).
Could you please explain how to setup the address areas?
M313_S317.JPG

M313_S317_config.JPG

According to the snapshots attached, is it accurate to conclude the following:
1. CPU 313C
Input area: PIW 0 - PIW 19
Output area: QIW 20 - QIW 29
2. CPU 317DP
Input area: PIW 0 - PIW 19
Output area: QIW 20 - QIW 29

What are the basic recommendations for allocating the PLC memory? And what is the 'consistency' listbox?
 
If someone is interested, the answer is YES.
I've double checked this and come to the conclusion:
1. The column 'partner address' represents the Input (2nd row) and Output (1st row) area of the Master (in my case CPU313C)
2. The column 'local address' represents the Input (1st row) and Output (2nd row) area of the Slave (CPU315DP)

The only thing which is not covered is the 'consistency' option. Does anybody have any idea??
 
"Consistency" defines an area of memory that will be updated together. Setting the consistency to all means that, in your case, all 20 bytes should be read and written together. If, for example, you write to PQW 0 you will open a constency window that will not be closed until the last byte of the area is written.

If you want to read/write to individual words in different places in the program then set the consitenct option to "UNIT" rather than "ALL"

Nick
 
Just a note, this will be standard IO, I and Q as far as addressing is concerned, no need for additional blocks and no programming referencing to PIW or PQW areas.
 

Similar Topics

Dose anyone have experience with Beckhoff FC3121 profibus master PCIe card connected to Siemens CP342-5 as a profibus slave? The data retrieved...
Replies
17
Views
4,797
Good morning, I am looking to establish a communication between one Profibus master and one Profibus slave. I downloaded the Profibus Master...
Replies
58
Views
14,470
Experts! Advice required S7300 CPU 2 DP 315 Master Slave Profibus.(2 CPU) In My application I have to send data from Master to slave and slave...
Replies
0
Views
1,939
Experts! Advice required S7300 CPU 2 DP 315 Master Slave Profibus.(2 CPU) In My application I have to send data from Master to slave and slave...
Replies
0
Views
2,334
Hello Guys, I have s7-315-2 PN/DP with integrated DP. I have no CP module. PLC should be DP master. ON other side there is basler device DECS250...
Replies
6
Views
3,479
Back
Top Bottom