Smallest SLC expansion

bluenoser337

Member
Join Date
Apr 2003
Location
Nova Scotia
Posts
391
I have a full 13-slot SLC5/03 rack and need to add one or 2(max) 16 point 120v AC input cards. What is the most compact, least expensive way to expand. Thanks!
 
If you have the room you could you replace the 13 slot with a 17 slot rack.

Edit..If you go this route you will need to check the power supply size.
 
Last edited:
Assuming you've not a communication module in the main chassis to be used as a master for a remote unit, you may only think to another SLC-type chassis (4 slots is the smallest) with an expansion cable and obviously with its Power Supply.

- fuzzy logic
 
If you have the room you could you replace the 13 slot with a 17 slot rack.

Edit..If you go this route you will need to check the power supply size.


Hi Bob,

I may be wrong but I have not seen a 17 slot for a SLC 500, only the CLX
 
I have a full 13-slot SLC5/03 rack and need to add one or 2(max) 16 point 120v AC input cards. What is the most compact, least expensive way to expand. Thanks!

Do you have any cards that are 8 point? you could change them to a 16 or a 16 to a 32 point I/O
 
genius...I do have some 8s and looked at that, but they are isolated outputs. I don't think a 16pt is available in an isolated version. I see there is a 2-slot rack (1746-A2)available. I have never actually seen one of these, and it doesn't appear in the I/O config selections, so I'm thinking it may not be an option. What was the A2 for...anyone know? Thanks!! Happy 4th to the US folks!!
 
It was the expansion chassis for very old fixed-syle SLC controllers, you cannot use it within your system.

- fuzzy logic
 
If you need to add then add a A4, then you will have two spares and having two spares will never hurt
 

Similar Topics

Hello friends. There is an int type, number that I got from the DataBlock. For example, the DataBlock address is Db1.dbw0. Here's what I want to...
Replies
32
Views
10,435
Good Afternoon, We have some new machinery and we are going to be networking the entire plant in 2019. Do you guys know of any small...
Replies
7
Views
1,703
I just ordered a TECO brand Smart Relay or micro PLC for a very small project in which space is at a premium. The application calls for logic...
Replies
8
Views
5,428
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
81
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
Replies
2
Views
95
Back
Top Bottom