How to diagnose a profibus fault?

uptown47

Lifetime Supporting Member
Join Date
Feb 2008
Location
Over there, next to those boxes
Posts
1,146
Hi all,

We have a machine that has about 20 inverters and several other devices attached to it via profibus.

Today we had a profibus fault. None of the drives or other devices would communicate. Every device showed a fault light. The diagnostic buffer was full of errors about Peripheral Words (read and write errors etc).

I've heard about devices that you can plug into networks to pin-point a specific location of a fault. Is there such a device for profibus? Or is there only the information that you get from the diagnostic buffer in Simatic Manager.

We think we've found the fault now. It looks like a linking bit of cable between two devices is faulty or getting interference but, in the future, we would like to be able to diagnose faults with a lot more confidence if possible.

Anyone any ideas?

Cheers

;-)
 
Profibus Troubleshooting is really hard .Mostly it because of the connectors or bad wires. You can buy profibus tester which will help you but it will cost you a lot of money
 
They make profibus connectors with led lights. This makes chasing down loose wires a lot easier. Here is a link to one.
http://www.dyertech.com/docs/Woodhead/DiagSim/DSUB-Profibus.pdf

Thanks for the link. That pdf says that the led's for fault finding work for "diagnostics versions only". Does that mean the device has to support diagnostics? ie. it wouldn't work on every device??

Profibus Troubleshooting is really hard .Mostly it because of the connectors or bad wires. You can buy profibus tester which will help you but it will cost you a lot of money

Do you know the part number of the tester? Or have you any other information on this?

Many thanks for all your help so far.

;-)
 
I don't have the slightest ideal what "diagnostics versions only" means.
It's been about 3 years since I used this type with the led on it and I don't remeber exactly who made it. I only did a quick google search for "profibus connectors led" and found this for you. The type we ordered had the led lights like that one but if there was a problem the light would turn to red. I will be glad to send out some emails and try to find the part number if you need futher help. Let me know.

I don't have the slightest ideal what "diagnostics versions only" means.
It's been about 3 years since I used this type with the led on it and I don't remember exactly who made it. I only did a quick Google search for "profibus connectors led" and found this for you. The type we ordered had the led lights like that one but if there was a problem the light would turn to red. I will be glad to send out some emails and try to find the part number if you need further help. Let me know.

P.S.
Terminator monitor indicates if terminator is missing (diagnostic versions only).​
I believe this refers to the last device being need to be set to the off position and one of their connectors with the built it diagnostics would indicate this.​
 
Last edited:
S7-400 controller connector has design defects
http://translate.google.com/transla...ttp://www.plc4good.org.ua/view_post.php?id=73
After 6 years of trouble-free operation of Siemens controllers, four series was occasionally lost connection to PROFIBUS-DP line with various devices. After a brief search had found the reason: the crank socket DP on the processor module...
or
PROFIBUS bus connector defect
http://translate.google.com/transla...ttp://www.plc4good.org.ua/view_post.php?id=72
After 5 years of operation of the equipment began to appear a problem of communication with the controller drives. After a detailed study of diagnostic and test the network device BT-200, was found fault bus connectors Profibus. In particular, in the OFF mode switch on the connector was a transitional floating a few hundred ohms resistance. It was decided to dismantle the bus connector....
conPR4.JPG
or
sequentially switch the terminator to ON - find the problem area network behind it.
 
in a similar situation in the past - i have seen Profitrace diagnose the problem within a matter of minutes.

http://www.procentec.com/profitrace2/

I've also seen eratic behaviour when the minimum 1m length between nodes wasn't adhered too.

Fluke's 125 Scopemeter is also a useful tool when diagnosing various Bus systems.
 

Similar Topics

Hi guys, Some of you may remember me mentioning a backup Profibus connection I have in my project. A quick recap: 1. Existing Profibus...
Replies
5
Views
3,235
Hi, Got a S7 400 talking over profibus DP to ET 200S machine stopped. Was reset before I got there. I looked at the History attached is the...
Replies
9
Views
4,811
I’m working on getting a Parallel Redundancy Protocol PRP system set up in a lab situation. The L73 PLC is in rack 4. 3 io racks are 1,2,3. I...
Replies
6
Views
746
Hi Everone, I want to know how we Diagnose Digital Input/Output module in S7 300 plC. Cpu 315-2dp Input module SM 321-32DIX24v Output module SM...
Replies
3
Views
2,110
Dear all, I downloaded program to ET200S and I have below fault on the diagnose. And CPU has below situation: Module available and o.k. Error...
Replies
2
Views
2,723
Back
Top Bottom