I need technical advice of using an interposing relay;is possible to connect two PLC through an interposing relay which will be located at 1000m and on the other side is just on the same switch room.
Reason of sing such arrangement
-This PLCs are owned by different companies(hosting company cannot allowed to connect its PLC they can only give out dry contacts(clients).
-I don't want to use flex I/O scanner.
Please advice my PLC is from Allan Bradley.
 
Mohamed,

What do you need to know? To select the correct relay, you will need to know what Output (and voltage level) you are going to use on YOUR PLC, and what Input voltage is available on the OTHER PLC.
 
Yes, it is possible. You may need other equipment besides a relay. I would use something else, such as a wireless relay.

If you must use standard off-the-shelf relay with 240 volt coil, and your wire is not larger than normal, then you also need to put in a step-up transformer near the relay, to increase the voltage back up to 240 volts.

Use large over-size wire to power relay, without a step-up transformer.

If your load is 1 Amps at 240 volts for 1000m, then the voltage drop for 10 AWG (American Wire Gage) wires will be 7.9 volts, and the voltage at the relay would be 232.1 volts.
 
Last edited:
Lancie1

From the specification of the coil it can operate at voltage of 125vac/240vac from your calculation the coil can be still energized
 
No, I think 2.5 mm is NOT equivalent to #10 AWG wire. You need about 5.2 mm^2 to produce voltage at 1000 meters of 232 volts through a relay load of 1 Amp. If you use a solid-state relay (in place of mechanical relay with coil), the load should be less than 1 Amp.

Here is a voltage-drop calculator so that you can calculate how many volts you will have at the relay.

2.5 mm^2 = 14 AWG
4.25 mm^2 = 12 AWG
5.2 mm^2 = 10 AWG
8.37 mm^2 = 8 AWG
 
Last edited:
No, a solid-state relay will operate with less current, so it will HELP the problem, but not completely solve it. You still need to increase your wire size from 2.5 mm^2 to about 5.2 mm^2 (or more).

Option: Use the smaller 2.5 mm wire, but add a transformer to increase the voltage back to at least 230 volts, so that relay will have enough voltage to operate. A transformer with small wire may be cheaper (than using larger 5.2 mm wire). The transformer option would cause extra trouble and make things less simple.

Using the smaller 2.5 mm^2 wire, your voltage would be about 219 volts (8% low). Use a booster transformer with at least three 2.5% taps (most have four taps below normal voltage, each at 2.5% increments . Set the secondary winding on the 3rd tap to increase the 219 volts back to 240 volts.

Another transformer option is a boost auto-transformer, which has a 240 volt primary and a 24 volt secondary. By wiring this as a booster, the primary voltage is boosted by 24 volts, which should get you back to about 243 volt range.
 
Last edited:
Mohamed,

The voltage decrease depends on actual power needed by relays. How much power does each relay use (0.5 Amps, 1 Amps, or more?) Note that the relay "inrush current" could be high - up to 50 Amps for small time period.

Yes, if you use the transformer option, you would need 1 small (250 volt-amp) transformer for each relay. Probably about $150 US for each transformer. Compare that to cost of increasing wire from 2.5 to 5.2 mm.

If you can find a relay with right voltage, you might try that. Probably you need solid-state relays with an operating range of 200 to 220 volts, assuming your actual voltage starts out at 240, and drops about 25 volts through the small wire.
 
Last edited:

Similar Topics

Why there is a requirement to connect interposing relay when we are using relay output type PLC?
Replies
14
Views
4,895
DEAR ALL, COULD ANYBODY help us for the following issue... how to wire the INTERPOSING RELAY CONNECTION TO PLC...
Replies
12
Views
3,203
In a project,I am using an Output Card where I have been advised to use 24VDC interposing relays to give output signals to field elements. I have...
Replies
9
Views
4,382
I read the following post: http://www.plctalk.net/qanda/showthread.php?t=49630&highlight=interposing Kid mentioned the 700HL interposing relay...
Replies
10
Views
5,235
I have read all posts in the forums, but still can't see the visual of the requirements of surge suppression on interposing relays. My application...
Replies
14
Views
8,657
Back
Top Bottom