i am trying to upload a project form IM151-8 PLC.
i can see the PLC and the HMI connected to it under display accessible nodes,now when i browse to blocks in the window it shows that there is no communication,partner does not respond.similarly when i select Upload station to PG, It shows that there is no communication. My PLC ip addess is 192.168.0.1,HMI IP address is 192.168.0.2 and my laptop IP address is 192.168.0.10.Please help.
 
As the IP address 192.168.0.1 is normally used for router login IP's I would suggest not to use that address
Check the subnet mask if possable
 
there is usually a setting on the HMI that tells it the IP of the PLC also (one for the HMI and one for the PLC)
This is my last guess sorry
 
as I said the HMI needs to be told to talk to the PLC It needs to know what the PLC's IP address is.
The AB PV's have an area that this needs to be set in.
Siemens also have this.
And OPC servers have this requirement.
it will be there - not clearly - these things never are
 
i meant to ask = you are using an industrial switch and not a router aren't you?
 
as I said the HMI needs to be told to talk to the PLC It needs to know what the PLC's IP address is.
The AB PV's have an area that this needs to be set in.
Siemens also have this.
And OPC servers have this requirement.
it will be there - not clearly - these things never are
i do not have any issue with the HMI communicating the PLC.my HMI is communication wtih PLC. But the only issue is PLC to PC communication.
 

Similar Topics

Hi guys, I have IM151-8 Siemens PLC, i want to connect it with Modbus and read/write on it using Modbus protocol. How can i do this? Do i need...
Replies
4
Views
2,535
Dear Colleagues, I am struggling with configuring the comms between G120 VSD and IM151-8 CPU over the Profinet. I have set the addresses and...
Replies
4
Views
2,225
Hello All, I've been reading all over about exchange data from CPU315-2DP and IM151-8F CPU (ET-200s CPU). End up what I just need to do for my...
Replies
2
Views
3,160
We have a system with a S7-400 and a WinLC-pc. The S7-400 has an ethernet cp. Both are communication on ethernet with SFB12 and SFB13. Now we want...
Replies
3
Views
2,487
Hey folks! I am about to program my first S7 system from beginning to end using a CPU I have never used before. My experience has been beginning...
Replies
13
Views
8,389
Back
Top Bottom