GregPLC said:
Tom, why would the voltage vary? current will vary based on motor frequency, but why would the voltage vary?
Greg
Current does NOT vary with frequency. Current varies with the torque required to rotate the load at the motor up to the point where the current limit of the VFD output is reached. This current may be limited by the VFD settings (the max current setting in the VFD during normal operation or starting) or by the thermal capacity of the VFD (the VFD max rated output current) or by the thermal capacity of the motor (the FLA is the point where the motor can't dissipate the heat generated by I-squared R losses).
Motors operate best at a constant Volts/Hz ratio. The typical VFD's inverter portion sets the operating voltage provided to the motor as a function of output frequency up to 60 Hz (in the US anyway). The normal Volts/Hz ratio is 7.6 Volts/Hz for a 460 Volt motor.
Motor speed is a function of frequency: synchronous rpm = (120 x Hz) / NumberOfPoles. Actual rpm = synchronous rpm - slip
The required torque to rotate the load is function of the load. Your agitator is probably a variable torque load. That means that the torque varies proportionally with the square of the speed, just like a centrifugal pump. The constant of proportionality is a function of the agitator characteristics, the fluid viscosity, the gearing, and so on.
Lets talk in general terms and for illustrative purposes only - I'd need a lot of data and a consulting contract to do the analysis for your specific system.
If your agitator is rotating in air: at 50% speed it may require 1% torque because of friction, say 10% current (because of motor magnetizing characteristics zero percent load isn't zero current) 50% voltage, and 50% frequency. At 100% speed it may require 2% torque because of friction, say 11% current, 100% voltage, and 100% frequency.
If your agitator is rotating in milk: at 50% speed it may require 25% torque because of friction and the power needed to induce fluid movement, 25% current, 50% voltage, and 50% frequency. At 100% speed it may require 100% torque, 100% current, 100% voltage, and 100% frequency.
If your agitator is rotating in ice cream: at 50% speed it may require 50% torque because of friction and the power needed to induce fluid movement, 50% current, 50% voltage, and 50% frequency. At 100% speed it may require 200% torque, 200% current, 100% voltage, and 100% frequency. Since the drive won't be rated to provide 200% current, either it will trip out or it will limit the speed to the point where motor torque and current are at 100% - in my example that would be 71% speed, 71% voltage, and 71% frequency!
If your agitator is "rotating" in solid ice: at a 50% speed command it would require infinite torque and infinite current. The VFD would put out 50% voltage at 50% frequency. Since the drive can't provide infinite current, it would provide as much as it could to try to accelerate the agitator, say 150%. If 150% torque is enough to break blades, your agitator will be trashed. If not, the VFD or motor will eventually over heat and trip out.
Always follow the cause and effect chain in your system. If your agitator blades are breaking, it is because something is physically inducing a load that exceeds their structural capacity, and the VFD is simply supplying the electricity that will provide the rotational torque that the motor must have to overcome that load and/or break the blade. The VFD can't break the blade all by itself - just imagine the agitator rotating in a vacuum!