Compactlogix Channel 0

cornbread

Lifetime Supporting Member
Join Date
Feb 2007
Location
madison, indiana
Posts
407
I'm trying to talk to a Compactlogix using channel zero. In RSlinx I have my USB 1747 driver set up and it auto configures just fine, however when I got to Who Active, I see nothing. Any pointers would be greatly appreciated.

I'm using RSlinx classic lite 2.57.00.14
 
Make sure the Auto-browse box is checked, or click Refresh, for RSLinx to try to browse the device.

Strictly speaking any point-to-point connection should ignore the Source and Destination bytes, but you might try configuring RSLinx Classic as a node address other than 0.
 
Aha... are you using a 1747-UIC ? Those are for DH485 protocol, which the CompactLogix supports but it's not the default.

The Autoconfigure, in that case, is the DF1 driver in RSLinx talking to the UIC device itself. There are specific configuration requirements for the 1747-UIC.

It's more likely that you need an ordinary USB/RS232 converter to connect using DF1 Full Duplex protocol to the CompactLogix.
 

Similar Topics

Hello, I am attempting to use the 1769-ASCII 2 Channel Module with a CompactLogix 1768-L43 Controller to connect to two AccuRange AR 700 lasers...
Replies
3
Views
7,941
Hi everyone, i have a compact logic 1769-L18 PLC and I'm using FTalk View ME for the display. I wanted to do some visualization on Grafana. At...
Replies
1
Views
83
Does anyone know what the data transfer rate for this series of CompactLogix PLC's? 1769-L24ER-QB1B to be exact. Cheers.
Replies
1
Views
88
Does this instruction calculate values during a single scan, or does it require number of scans based on element count in the array? For Example...
Replies
3
Views
109
Hello all, and thank you in advance for any assistance you may be able to provide! This is my first post, so if I need to reformat or change...
Replies
6
Views
380
Back
Top Bottom