dcooper33
Lifetime Supporting Member + Moderator
Hi all,
I was asked to change some stuff on the Runtime Security of a couple of PV+ 1000's that run on two different extruders, which function mostly as user interface for temp. controls and monitoring of the winder safety devices.
One of the screens was running a runtime file that must have been <ver. 5.0, because when trying to restore the .mer in the 5.1 studio on the laptop, a message popped up saying (paraphrase) "runtime file created with a software version that does not support restoring runtime app". There was a .med file in HMI projects file of the same filename as the .mer file in question, and all the screens, tags, and comms looked the same, so I went ahead and made the changes needed and created a runtime file from that project, and, unfortunately, overwrote the original .mer file
Then, when loading the file to the terminal, I noticed that the pv+ couldn't load the file, because it was running firmware 5.00.00.25. So I did a firmware upgrade to 5.10.00.09, and that went ok, but after restarting the terminal I ran into some comm problems.
The term. communicates with a PLC 5/20 on DH+, and that continues to work ok, the problem is with the Ethernet communication between the terminal and the Watlow EZ zone temp controllers. When I go to either of the screens that contain temp. controller tags, I get error messages saying something like (paraphrase again) "FactoryTalk: the object (Watlow.EZzone1.Setpoint) is no longer available". All the setpoint and temp. readout displays show "error"
The I.P. addresses are still there for each controller, and there is still a KEPServer OPC server in the project tree in the Studio.
I did notice in the HMI project folder for each project that there is a KEPServer folder in the the project that didn't need a firmware upgrade, but there isn't one in the other project folder.
Is this something that could have gotten lost when the project was imported from RSView 4.0 or whatever it was to FT View 5.1?
Sorry for the long-winded post, I've never worked with Kepware before, and never ran into a problem like this, and I wasn't sure what info would be relevant.
Thanks in advance for any help.
Cheers,
Bmac
I was asked to change some stuff on the Runtime Security of a couple of PV+ 1000's that run on two different extruders, which function mostly as user interface for temp. controls and monitoring of the winder safety devices.
One of the screens was running a runtime file that must have been <ver. 5.0, because when trying to restore the .mer in the 5.1 studio on the laptop, a message popped up saying (paraphrase) "runtime file created with a software version that does not support restoring runtime app". There was a .med file in HMI projects file of the same filename as the .mer file in question, and all the screens, tags, and comms looked the same, so I went ahead and made the changes needed and created a runtime file from that project, and, unfortunately, overwrote the original .mer file
Then, when loading the file to the terminal, I noticed that the pv+ couldn't load the file, because it was running firmware 5.00.00.25. So I did a firmware upgrade to 5.10.00.09, and that went ok, but after restarting the terminal I ran into some comm problems.
The term. communicates with a PLC 5/20 on DH+, and that continues to work ok, the problem is with the Ethernet communication between the terminal and the Watlow EZ zone temp controllers. When I go to either of the screens that contain temp. controller tags, I get error messages saying something like (paraphrase again) "FactoryTalk: the object (Watlow.EZzone1.Setpoint) is no longer available". All the setpoint and temp. readout displays show "error"
The I.P. addresses are still there for each controller, and there is still a KEPServer OPC server in the project tree in the Studio.
I did notice in the HMI project folder for each project that there is a KEPServer folder in the the project that didn't need a firmware upgrade, but there isn't one in the other project folder.
Is this something that could have gotten lost when the project was imported from RSView 4.0 or whatever it was to FT View 5.1?
Sorry for the long-winded post, I've never worked with Kepware before, and never ran into a problem like this, and I wasn't sure what info would be relevant.
Thanks in advance for any help.
Cheers,
Bmac