Using DH+ with paneliew plus

Join Date
Sep 2008
Location
rockford,il
Posts
26
I have a panelview plus with a DH+ module attached and i cant get DH+ to come up as a selection in the The configuration window in the terminal settings. I have even tried adding DH+ to the network tree in rs view me and downloading using ethernet. And still cant get it to come up with DH+ as an option. Has anyone else had this problem?
 
I'm not sure where you are trying to set it up, but you should be using the communication configuration under the application tab, then under the runtime setup.

If you right-click on the RSLinx enterprise icon, you can select "Add Driver". That pulls up a window that allows you to pick from a number of drivers. DH+ is one of the options there.
 