SCHNEIDER PRM Module with M340

mosama

Member
Join Date
May 2009
Location
Egypt
Posts
182
I'm going to use PRM module (TCS EGPA23F14F) with M340 PAC to communicate with S7300 CPU314C-2DP. My question is: should I use I/O scanner module (NOE module) for M340 or I can use only the integrated ethernet port of the CPU ???
 
I don't think you have an option - If I recall when I considered using this device I needed to use the IOScanner service. Since the M340 processor Ethernet port does not support IOScanner, then you would have to use an NOE0100/0110 device (or maybe a NOC0401 - this has IOScanner, but I don't know if it will work).
 
Thank you Robert. The user guide of the PRM module states that:

"The configuration must include a Modbus TCP Ethernet port to scan the PRM. It can be an Ethernet communication module (ETY or NOE) or the Premium / Quantum CPU embedded port where an IO scanner can be configured."

I just wanted to confirm this. Thanks again
 
What is required for this PRM module (TCS EGPA23F14F), the catalog says:
TCX PBS CA 100 = PROFIBUS DP connection cable - 100 m
490 NAD 911 03 = Line terminator
490 NAD 911 04 = Intermediate Connection
490 NAD 911 05 = Intermediate connection and terminal port

Which one should I use of these terminators ???

Thank you
 
What is required for this PRM module (TCS EGPA23F14F), the catalog says:
TCX PBS CA 100 = PROFIBUS DP connection cable - 100 m
490 NAD 911 03 = Line terminator
490 NAD 911 04 = Intermediate Connection
490 NAD 911 05 = Intermediate connection and terminal port

Which one should I use of these terminators ???

Thank you

Can someone tell me which terminators are needed for this module ??
 
The PRM module is connected to the plc through the ethernet port so a standard cat5 cable is used on this side.
On the Profibus side you can just use standard Profibus cable and connectors (except if connecting to TeSysU then you need special 4 wire cables and connectors)
 

Similar Topics

I have a Schneider PRM module connected to an M340 processor via an NOE 110 Ethernet card. I have several Profibus slaves in the form of Siemens...
Replies
0
Views
2,091
hi to all, have anyone tried to communicate Schneider PM800 to a ML1400 through rs485? i am having an issue with it just receiving message...
Replies
1
Views
51
Hello All, I am stumped on how to convert a %MW to a %MF using Machine Expert Basic and a Modicon M221. The help files show a word to a double...
Replies
4
Views
180
Hi, Is Control Expert V15.0 supposed to support multiple monitors? I'm running Control Expert V15.0 on my host Windows 11 PC, connected to two...
Replies
1
Views
92
Everything was working fine, but suddenly CPU went into error mode, and the ERR and TER LEDs lit up. Now I can't download or connect with the PLC...
Replies
0
Views
107
Back
Top Bottom