Hi Experts!
I have some limited resources. I need help on the following idea?
I have 10 slot chasis and now all the modules place. I have four Analog signal extra and have one point on the module. First i mentioned these signals are used just for reading the values and pass it to HMI. No concern with controling the bit on and off. I have a 4 way selector switch if i attached four signals to respective deck of selector switch and pass the common point to the module. when i want to read the values i select the switch and values passes to the HMI and save it into the user defind tag.
When chnage the selector switch from one position to the other a break occur then what happen? Is it dengerous for the module? or if any one have idea please guide me?
Regards
 
hi
I download the article and read but there is no idea how to use one channel with four inputs via selector? is it used?
Regards
 
The open circuit on an analog input is not dangerous. It will either go to zero if it's a mA input, or if it's a voltage input it may go to some arbitrary value (or zero) depending on how the input module is wired externally and internally. But it should not damage the module.

You may need to make changes in your program to account for the break, so you don't alarm the system, or the sudden change in the analog value may cause unexpected program results, etc.
 

Similar Topics

Hi friends; I make a circuit and now i want to connect with analog module ALG223. Plz guide me how i wire up? Terminal number 2 of module gives me...
Replies
2
Views
2,628
Hi friends; Is Rosemount transmitter model 3051 smart transmitter compatible with ALG223? Regards
Replies
1
Views
3,061
Hi all Is it better to set the GE IC694ALG223 analog card to 0-20mA and then scale it in a function block. Even though the device attached is...
Replies
1
Views
1,944
Hi Everyone, i was hoping for a little help with this module. i have data that needs to be read from a different plc through the Modbus plus...
Replies
9
Views
124
Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
Replies
5
Views
105
Back
Top Bottom