Ok, I am needing to send some data from one GE 90-30 CPU374 to another one. Means would be over Ethernet. What is the best way to do this? I know in a Control Logix I would use a message instruction to message an array over. However I can not find something like that in the GE instruction set. I see where the processors support Modbus TCP/IP but again don't see an instruction that would read or write any data. Am I just missing it?
 
EGD is an option, however there is also the COMMS_REQ instruction that is equivalent to a message instruction in AB.

However....read up on on the COMMS_REQ manual, it's a ridiculous pain to configure.
 
EGD is an option, however there is also the COMMS_REQ instruction that is equivalent to a message instruction in AB.
However....read up on on the COMMS_REQ manual, it's a ridiculous pain to configure.
EGD is the best option, however.
COMM_REQs are not really very difficult. They use between 5 and 10+ consecutive %R addresses. Based on the value of these registers the Communications Request knows what to do. One just fills in the proper values, from the manual, use a "1_Shot" to enable the COMM_REQ Function Block and watch for a "1" to come back to the programmed "Status" register. :)
The "Painful" part is that one must read the manual. (n)
 

Similar Topics

I had a comms fault between my VFD and Controller (5069-L320ERS2) that started about a month ago and happened maybe once a day to now where it...
Replies
1
Views
249
Hi. I am having trouble establishing comms between an slc5/04 and panel view plus 7 via a PLX51-net-eni. The set up is: 5/04 Channel 0 DF1...
Replies
8
Views
872
Hi, Does anybody have experience with Ethernet/IP-CIP Safety comms between 2 different brands of PLC's I have a project with 1 Safety Allen...
Replies
13
Views
3,498
I was just wondering if anybody had any experience setting comms between Wonderware Web Studio and an Lantronics XPORT-EIP comm card. I’ve...
Replies
1
Views
1,362
Hi all, I have the following setup: 3 remote stations that will run a micro820 plc each one. 1 main station that will run a compactlogix plc...
Replies
4
Views
1,799
Back
Top Bottom