the Blue NC contacts were back
What you're describing is (if I recall correctly) a 'configuration mismatch' icon in RSNetworx for DeviceNet.
Most configurable DeviceNet products have an internal read-only parameter called a Configuration Consistency Value (CCV). It's just a simple checksum of the various configuration parameters in the device.
When RSNetworx for DeviceNet browses a network, it reads the Device Identity and the CCV, and uses those to graphically tell you about the devices on the network.
If a device is actually a different Identity, you get an icon (and a diagnostic log entry) indicating a device identity mismatch. This would happen if you replaced a 15 ampere E3 with a 100 ampere E3, for example, or swapped a photoeye for a limit switch.
If the CCV is different between the online device and the offline file, you get a "configuration mismatch" icon, indicating that the configuration in the RSNetworx file and the configuration in the device are not the same.
RSNetworx doesn't know which one is newer, or which one is "correct". It just knows if they are the same or not.
I don't remember for sure which of these icons are red or yellow or blue. RSNetworx Help will tell you.
In your case, you must have resolved the identity mismatch by updating RSNetworx, or you downloaded a configuration that resolved the configuration mismatch.
Glad you got it working !