aradhonline
Member
Our System configuration
1756-A4 with !1756-l72!1756-cn2r!1756-rm!1756-en2t!
1756-A4 with !1756-l72!1756-cn2r!1756-rm!1756-en2t!
stratix 2000 series Ethernet switch 1783-us08t (For FTSE communication and EN2T looping)
1794-acnr15 flex i/o's
So far redundancy is Ok and with 19.53 Flash and we have SYNC displayed on the secondary.
FTSE we have configured as OPC client with Local RSlinx as OPC master and configured Topic in OPC /DDE Topic Configuration.All Ok with the communication.
The Problem..
When we switchover the controller say we tripped one We have a change over time of 12 seconds in FTSE. Ie Value updates only after 12 seconds.Previous value is retained though.
But for digital outputs which are on control-net is having bump less transfer on switchover..We played with timeouts and Polled messages parameters in RSlinx Topic Configuration but no use.I really think 12 seconds is hard for the cost we have spend ..And we are stuck right here ..
Is that problem with the switch ..I mean do we need managed switch ?.Or with OPC server ie any other method of connection ?.
Any Type of Help would be Highly Appreciated ...Thanks alll.
1756-A4 with !1756-l72!1756-cn2r!1756-rm!1756-en2t!
1756-A4 with !1756-l72!1756-cn2r!1756-rm!1756-en2t!
stratix 2000 series Ethernet switch 1783-us08t (For FTSE communication and EN2T looping)
1794-acnr15 flex i/o's
So far redundancy is Ok and with 19.53 Flash and we have SYNC displayed on the secondary.
FTSE we have configured as OPC client with Local RSlinx as OPC master and configured Topic in OPC /DDE Topic Configuration.All Ok with the communication.
The Problem..
When we switchover the controller say we tripped one We have a change over time of 12 seconds in FTSE. Ie Value updates only after 12 seconds.Previous value is retained though.
But for digital outputs which are on control-net is having bump less transfer on switchover..We played with timeouts and Polled messages parameters in RSlinx Topic Configuration but no use.I really think 12 seconds is hard for the cost we have spend ..And we are stuck right here ..
Is that problem with the switch ..I mean do we need managed switch ?.Or with OPC server ie any other method of connection ?.
Any Type of Help would be Highly Appreciated ...Thanks alll.