Hey guys I have a PowerFlex 4 22A-D6P0N104 3 phase in/out 415v.

I have a fault that comes up only between 40-50 Hz after around 10 minutes of F3 Power Loss?? It runs OK under 40Hz. I am at a Loss as to why this is happening, I have tested incoming voltage and appears stable at 415v.

Any comments?

thanks
hazey
 
My guess would be you have lost one of your incoming phases. Possibly by a loose wire or blown fuse, etc. A single phase is probably enough to maintain the buss voltage up to 40Hz, but then your power demand probably surpasses what the single phase can supply.

Have you checked phase to phase between all phases right at the drive terminals?
 
Generally speaking, the power loss fault is an indication the drive can't maintain buss voltage. Since your certain all three phases are fine this narrows the options pretty quick. You should monitor the bus voltage over the that 10 minute span from power up to failure and see if it is just gradually dropping (just monitor d005). You should also check the setting for the trip thresholds.

It may simply be a bad drive. One of the caps may be bad and no longer taking a charge or a bad buss to cap connection. Is this a new installation or something that has been running for some time?
 
Yes new installation, I did check Buss voltage but only briefly, not the whole time. Buss Voltage was 610-620v. I will check from startup to failure in the morning. The 2.2kw motor is on a seed grader and is fully loaded.

thanks

hazey
 
Yes, the big point of interest is where the buss voltage is at around the time it goes south. Looking at my prior post, I also forgot to include possibly an open bridge on your rectifier. We can rule out that by putting an amp probe on all three feeds and verifying you are drawing ballanced current on all of them.
 
Just to close this out I had to install 4kw drive on 2.2kw motor to fix problem, must have been load related?

thanks

hazey
 

Similar Topics

Hello everyone, I'm new here. First of all I just want to say that you guys are very knowledgeable and reading your posts on here has saved my...
Replies
4
Views
154
Hi to all. We need to change a bad powerFlex 525 to a new one. How do you save the configuration to install in the new one? Thank you all for...
Replies
5
Views
207
Im trying to teach a couple of labs on VFDs at a community college. We have some motor control trainers with P525s and 3 phase motors from...
Replies
0
Views
123
So I'm replacing a terminal block on the inverter board for a 755. I'm wondering if anyone knows what conformal coating would be best? I'm not...
Replies
1
Views
93
I have recently started at a new plant, and we use a lot of power flex 40 drives for conveyors. on my fiorst day they sent me to start a line...
Replies
11
Views
224
Back
Top Bottom